hmspe
Senior Member
- Location
- Temple, TX
- Occupation
- PE
fido said:Correct me if I am wrong on this, but a kwh is a kwh. At the higher voltage for the same load, would you not use less kwh, therefore have a less expensive electric bill for any given load? I recently came across this exact situation on a job and gave the owner the choice. He went with the 277/480.
How do you get the KWh being lower? If you have a 10KW heater it draws 10 KW regardless of the voltage, right? This assumes the heater is rated at the voltage it is installed on. Run it for an hour and you have 10KWh Take a 5 horsepower motor. At 208V the Table 430-150 (the 1999 NEC is what's handy) FLA is 16.7A. 16.7A X 120V X 3 phase = 6012VA. At 480 the FLA is 7.6. 7.6A X 277V X 3 phase = 6316 VA. There's a lot of rounding error in these calcs, but for practical purposes the VA (and KVA) is the same for a 5 HP motor regardless of the voltage it's wound for. When the volts go up the amps come down for equivalent loads.
There are far too many unknowns to make absolute statements, but for equvalent equipment sizes (same wattage on lights, same tonnage on AC, etc.) the KWh drawn will be the same regardless of voltage. If the rate the utility charges per KWh is the same at all voltages the bill won't change because the power usage won't change.
There are areas in a system that might make a difference. Because the current will be higher at 120/208V the heat losses in the wires will be higher. On the other hand, when you add a step-down transformer to a 277/480V system you have losses in the transformer that would not exist on a 120/208V system.
I tend to stay with 120/208 whenever I can. In my opinion the total installed costs are about the same [larger wire and conduit, and higher ampacity on the service at 120/208; added transformers and a second set of (more expensive) panels at 277/480]. For a properly sized and installed system the overall I2R losses will be about the same. You don't pay for space or cooling for stepdown transformers. 120/208 is much safer for the janitor who gets told to swap out a fuse.
All that said, the building described would be a good candidate for 277/480V because of the lengths of the runs. The issue will be whether there is room for transformers and panels. The only way we could make things work on one elementary school I did was to put the transformers on the roof. Not ideal in Arizona.
Martin