kingpb said:A 75kVA 480-208Y/120V Xfmr will have approx. 143W of losses. So, if you have more then 9 motors ( 9 x 17.3W = 155W) for each 75kVA transformer your installation would pay for itself by going to 480V instead of using just 208V. Increased light fixtures on a circuits, plus lower overall heat, would reduce cooling some.
I don't get that statement. The SES would be at 208v, so transformer losses are on the power company's tab.