mjr5097
- Philadelphia, PA US
For reasons I'm not going to describe, we ended up with a generator supplied circuit that comprises of 150' of (3) 600 XHHW kcmil/phase in conduit, transitions to (3) 4/0 RHW-2 cables inside a junction box for a length of about 6ft then transitions back to another 200' of (3) 600 kcmil/phase in conduit. It's protected by a 1200A breaker.
One interpretation is that the junction box is not considered a raceway and the free air rating of 405A is applicable for each of the 90C RHW-2 with its 90C rated terminations.
Others do consider the junction box a raceway, with each RHW-2 only good for 260A.
A third opinion is that the raceway vs not a raceway question is irrelevant based on the 310.A.2 exception for the 6ft of RHW-2.
I'm curious where the experience here falls with this question.
Thank you!
Thank you!