If you look at electric cooktops and wall mounted ovens with electronic controls none of them use a neutral.
For example here are the specs for a GE induction cooktop:
http://products.geappliances.com/Ma...?RequestType=PDF&Name=220593_pp945wmbm_r2.pdf
Here is a link to the complete installation instructions that say the unit does not use a neutral:
http://products.geappliances.com/MarketingObjectRetrieval/Dispatcher?RequestType=PDF&Name=31-10637-3.PDF
I believe if you look at the power supply for your computer you will see 100-240V AC 50/60hz.
Most electronic powers supplys are intelevolt these days, like a lighting ballast.
I think they are using the same controls in a range as the cooktop units, or at least they can.
Also on the 240V heaters note, it is common for them to have electronic controls that run off of 240V.
See:
http://www.cadetco.com/show_product.php?prodid=1025
I do not pull a neutral to a heater so it can have an electronic control.
I am not saying start running a 2 wire + ground to a stove in new construction, I will still run a 4 wire until the standard changes.
However there is no logical reason to design a new stove to use a neutral.
In a remodel situation with a 3 wire SE cable with a bare conductor it might be preferable to order a 240 V stove rather than continue using the bare conductor as a neutral/equipment grounding conductor.
The next logical step would be to remove all exceptions for 10-50 and 10-30 receptacles and using a neutral as an equipment grounding conductor from the code. Since a 10-50 receptacle can be converted to a 6-50 and appliances are readily available for the same price that are straight 240.
Appliance manufacturers are driven by the NEC they would catch on quickly and all stoves would just come with a unused terminal for a neutral to land if it is present in the cord (as many do already).