- Massachusetts
I think you really mean that the majority of the AHJs will get it wrong in a way that makes sense and probably supports the original CMP intent.
That is not the same as getting it right. :angel:
:thumbsup:
Intent may mean nothing to some of the volume posters on this forum, but it carries a lot of water in the real world. :thumbsup:
SolarP which thing do areas adopt? The Code, the intent or the CMP comments?
The NEC is supposed to be understandable and enforceable by using the NEC. You should not expect every installer or even inspector to be going through the intent, the CMP comments etc in order to understand the code and in this case to ignore what is written in it.
I know you are very sure you are right in your interpretation and your knowledge of the intent. Well I agree with you about the intent, I disagree with your interpretation.
May have been your intent but the words you chose did not convey it.![]()
Those AHJs are correct. Identified is a defined term....
Looking at the code making process and listening to the CMP members it is very clear that the intent was that equipment used in rapid shutdown needed to be listed and identified electrical equipment but that was the extent of it. Some AHJs interpreted it to mean that the equipment needed to be listed and identified specifically for use in rapid shutdown.
Labeled vs. identified. The NEC 2017 requirements for “listed and labeled” rapid-shutdown equipment meaningfully revises NEC 2014, which requires “listed and identified” equipment. Article 100 defines the term identified as “suitable for the specific purpose, function, use, environment, application, and so forth.” By contrast, the definition of labeled in Article 100 “indicates compliance with appropriate standards or performance in a specified manner.” The latter is more prescriptive and narrowly defined than the former.
In practice, this means that installers can use off-the-shelf electrical components to meet NEC 2014 rapid-shutdown requirements so long as the conditions of use are consistent with the equipment ratings. For example, under NEC 2014, you could locate a contactor combiner at the edge of a PV array and use this to meet Section 690.12 as long as the combiner was rated for the outdoor environment and the PV voltage and current characteristics. NEC 2017 will require that this contactor combiner be specifically listed to a rapid-shutdown PV array standard and labeled accordingly. Revised language in 690.12(D) states: “Equipment that performs the rapid-shutdown functions, other than initiation devices such as listed disconnect switches, circuit breakers or control switches, shall be listed and labeled for providing rapid-shutdown protection.”
This is an important distinction. Some jurisdictions— including New Jersey, New Mexico and Washington—have misinterpreted NEC 2014 requirements and asked installers and vendors to prove that rapid-shutdown solutions comply with a rapid-shutdown safety standard. As of today, no such standard exists. Until the NEC 2017 is adopted, there is no requirement that equipment used for rapid shutdown be listed and labeled specifically for the rapid shutdown of PV arrays. Installers can use any listed equipment to provide rapid shutdown, so long as they field the equipment in a manner consistent with the product listing.
If you view the Code as a Platonic ideal, I realize that the intent and opinion of the Code-Making Panel is irrelevant to enforcement. However, this is how the person who led the working group that originally developed 690.12 describes the difference between the listing requirements in NEC 2014 vs NEC 2017:
Source: NEC 2017 Updates for PV Systems
So what you're saying is that it is about to get much worse; that the misinterpretation is about to be enshrined in the code. Now the equipment will have to be listed for rapid shutdown, and there's still no standard to list it too!!
I could've sworn that the intention is that the equipment just has to be listed in general. And not necessarily listed specifically for rapid shutdown.
So for instance, a microinverter or AC module system already would comply, with a standard AC disconnect, and without any rapid shutdown specific equipment. Shut off the building power in general, and the module energy is limited to the input of the microinverter. And this would still comply, even if you are using modules, microinverters, and AC balance of systems components that have been kicking around in a warehouse since 2008, before rapid shutdown was even a concept.
Some people believe that their interpretation is correct against all odds. Even if they are the only one in the USA who interprets it that way they are right and everyone else is wrong. I have talked to these people and there is no proof you can give them that they are not interpreting the code correctly. But for others who are open to a different interpretation, showing them the basis for the NEC wording can change their mind.
But not you right?
Again I do not disagree with you about what the submitter's intent was.
But intent is not enforceable, only the adopted words are the code and regardless of how well you know the intent it does not change the adopted code.
Thought I was reading a quip from a fortune cookie there for a moment.The question of intent is relevant when there is ambiguity, but not when the words unambiguously go against the intent. ...
The question of intent is relevant when there is ambiguity, but not when the words unambiguously go against the intent. Each AHJ has a certain amount of freedom to approve things that go against the wording but match the intent, but that approval does not change the meaning of the words.
They are not AFAIK allowed to reject something that matches the words.
Building or Structure?
The NEC definition of structure is broad: “that which is built or constructed;” a building is defined as a “structure that stands alone or that is cut off from adjoining structures by fire walls with all openings therein protected by approved fire doors.” This could be a house (a dwelling), garage, office building, factory, or retail space, but not a carport or freestanding gazebo. A building is a structure, but not all structures are buildings.
This matters because Section 690.56 requires a label identifying power sources and indicating the location of the PV system disconnecting means when PV systems are on either a building or a structure, thus applying, for example, to both a home or a carport. However, the rapid shutdown requirements of 690.12 apply only to PV systems on buildings—and thus do not apply to a carport or ground-mounted system. The 690.31(G) requirement for DC circuits to be in a metal raceway or type MC applies to circuits inside both buildings and structures. And a big change in the 2014 NEC was the removal of “on or penetrating a building” from Section 690.11, effectively extending DC arc-fault protection to all PV systems.
Bad logic, as previously discussed. Under the 2014 NEC definitions, a building is part of a structure, and every structure is one or more buildings.Home Power said:. . . A building is a structure, but not all structures are buildings.