With 2017 NEC that is a possibility.Maybe it,s in a crawl space.
And in most instances if it won't reach you probably have a violation of 300.14.If that neutral wont reach the load side neutral terminal of the GFCI, then it is needed. If not, you need the pigtail extension.
And in most instances if it won't reach you probably have a violation of 300.14.
Where have all the butt connectors gone?In the photo attachment here, drawn from a actual
wired box. is the Neutral wiring pigtail connection
needed? or just a waste of resources? bottom of page.
why not bring the neutral wire directly to the screw terminal?
Read 310.14 carefully. I don't think you can run 3 inches of conductor into a box and then splice a pigtail on to get 6 inches of conductor. Won't say I've never done it, but don't think it complies with 310.14.If it wont reach pigtailing an extension on it makes it compliant again.
Read 310.14 carefully. I don't think you can run 3 inches of conductor into a box and then splice a pigtail on to get 6 inches of conductor. Won't say I've never done it, but don't think it complies with 310.14.
Copied from 2014:You mean 300.14. I did. Unless the 11+ NEC are diff from the 08, it says "at least 150mm (6") of free conductor...". Doesnt say that conductor must be unspliced or continuous. If splices/wirenuts werent allowed, 90% of old boxes would fail this code section.
I don't see splices being a part of "free conductor" if in the first 6 inches. Don't know if wording has changed since 08 or not.At least 150 mm (6 in.) of free conductor, measured from the point in the box where it emerges from its raceway or cable sheath...
Copied from 2014:
I don't see splices being a part of "free conductor" if in the first 6 inches. Don't know if wording has changed since 08 or not.
Q. We cut our wire too short in a few outlet boxes so I spliced on a couple inches of conductor so that I had the required 6 in. of free conductor at each location. The inspector says the free conductor must be "unspliced." Is he right?
A. No. He is correct that the NEC requires at least 6 in. of free conductor be available from the point in the box where the conductors enter the enclosure [300.14]. However, nowhere in this rule does it require that the free length of conductor be unspliced.
http://www.ecmweb.com/qampa/stumped-code-7
I believe 300.14 is unchanged from 08 to 14, probably 17 too.
Lets say the trim, cabinet, tile or drywall guy rotozips your wire (noob traced inside the box). Now you have 4" of wire instead of 6".
You going thru the effort of fishing in new wire, or add a wirenut and splice and go about your day?
This also leads to 334.30 re: service loops and stapling requirements, another fun section I like to debate.