is a pigtail connection needed here?

Status
Not open for further replies.
In the photo attachment here, drawn from a actual
wired box. is the Neutral wiring pigtail connection
needed? or just a waste of resources? bottom of page.
why not bring the neutral wire directly to the screw terminal?
 

Attachments

  • circuit.jpg
    circuit.jpg
    76.7 KB · Views: 4
I agree the splice was probably due to a damaged wire or something but my question is, why they are protecting the fixture with a GFCI?

Roger
 
In the photo attachment here, drawn from a actual
wired box. is the Neutral wiring pigtail connection
needed? or just a waste of resources? bottom of page.
why not bring the neutral wire directly to the screw terminal?
Where have all the butt connectors gone?
Long time passing.
When will we ever learn?
 
If it wont reach pigtailing an extension on it makes it compliant again.
Read 310.14 carefully. I don't think you can run 3 inches of conductor into a box and then splice a pigtail on to get 6 inches of conductor. Won't say I've never done it, but don't think it complies with 310.14.
 
Read 310.14 carefully. I don't think you can run 3 inches of conductor into a box and then splice a pigtail on to get 6 inches of conductor. Won't say I've never done it, but don't think it complies with 310.14.

You mean 300.14. I did. Unless the 11+ NEC are diff from the 08, it says "at least 150mm (6") of free conductor...". Doesnt say that conductor must be unspliced or continuous. If splices/wirenuts werent allowed, 90% of old boxes would fail this code section.
 
You mean 300.14. I did. Unless the 11+ NEC are diff from the 08, it says "at least 150mm (6") of free conductor...". Doesnt say that conductor must be unspliced or continuous. If splices/wirenuts werent allowed, 90% of old boxes would fail this code section.
Copied from 2014:
At least 150 mm (6 in.) of free conductor, measured from the point in the box where it emerges from its raceway or cable sheath...
I don't see splices being a part of "free conductor" if in the first 6 inches. Don't know if wording has changed since 08 or not.
 
Copied from 2014:
I don't see splices being a part of "free conductor" if in the first 6 inches. Don't know if wording has changed since 08 or not.

Q. We cut our wire too short in a few outlet boxes so I spliced on a couple inches of conductor so that I had the required 6 in. of free conductor at each location. The inspector says the free conductor must be "unspliced." Is he right?

A. No. He is correct that the NEC requires at least 6 in. of free conductor be available from the point in the box where the conductors enter the enclosure [300.14]. However, nowhere in this rule does it require that the free length of conductor be unspliced.

http://www.ecmweb.com/qampa/stumped-code-7

I believe 300.14 is unchanged from 08 to 14, probably 17 too.

Lets say the trim, cabinet, tile or drywall guy rotozips your wire (noob traced inside the box). Now you have 4" of wire instead of 6".

You going thru the effort of fishing in new wire, or add a wirenut and splice and go about your day?

This also leads to 334.30 re: service loops and stapling requirements, another fun section I like to debate.
 
Last edited:
Q. We cut our wire too short in a few outlet boxes so I spliced on a couple inches of conductor so that I had the required 6 in. of free conductor at each location. The inspector says the free conductor must be "unspliced." Is he right?

A. No. He is correct that the NEC requires at least 6 in. of free conductor be available from the point in the box where the conductors enter the enclosure [300.14]. However, nowhere in this rule does it require that the free length of conductor be unspliced.

http://www.ecmweb.com/qampa/stumped-code-7

I believe 300.14 is unchanged from 08 to 14, probably 17 too.

Lets say the trim, cabinet, tile or drywall guy rotozips your wire (noob traced inside the box). Now you have 4" of wire instead of 6".

You going thru the effort of fishing in new wire, or add a wirenut and splice and go about your day?

This also leads to 334.30 re: service loops and stapling requirements, another fun section I like to debate.

Been there and done that a few times, also spliced onto existing short conductors.

Don't mean an inspector will see it that way either.

Been a long time ago, but we once had an existing masonry wall building they decided to cover walls with an insulating material. Wiring was all surface raceways, our job was to put extension rings/mud rings on boxes to bring them to the new finish surface. Inspector made us pull new conductors if we couldn't get three inches out of the opening of the box - which is also a requirement if box opening is less then 8 inches.
 
Does seem like the 6" is intended prior to the splice

At least 150 mm (6 in.) of free conductor, measured from the point in the box where it emerges from its raceway or cable sheath, shall be left at each outlet, junction, and switch point for splices or the connection of luminaires or devices.

But also looks like this overrides in cases up to 3 gang boxes

Where the opening to an outlet, junction, or switch point is less than 200 mm (8 in.) in any dimension, each conductor shall be long enough to extend at least 75 mm (3 in.) outside the opening.


so a box that is 1 1/2" deep box would require 6" & 3 1/2"deeper boxes would need additional conductor -- though I tend to agree an extension of a short wire should comply with code.
 