Isaiah
Senior Member
- Location
- Baton Rouge
- Occupation
- Electrical Inspector
Some of us design-build a majority of our installations, but yes such calculation should be done before selecting key items or you could end up having to change things.
After you been doing this long enough you kind of get the feel to what needs looked into for SCC and what doesn't. Smaller conductors and length of run over 25 feet will drop available current at the end of the run pretty quickly compared to large conductors at those shorter lengths. Plus you also have service and feeder conductors that factor in before you have a starting SSC value to apply to your branch circuit when installing something to existing panelboard. A lot of HVAC equipment especially "residential grade" stuff is only rated for 5kA, usually that is not a problem in dwellings or light commercial locations anyway but can be situations where it doesn't hurt to double check.
Nice feedback. This particular unit is an industrial type HVAC with MCA of 70A at 480V 3 phase. They ran number 3/C w/Grd, 4AWG, XHHW-2 for a distance of around 100’, which looks good from an ampacity and VD standpoint but wasn’t sure how to calculate the SC when asked
Sent from my iPhone using Tapatalk