Fred B
Senior Member
- Location
- Upstate, NY
- Occupation
- Electrician
It should be marked somewhere, and should be all the way to the last panel board supplying the branch circuits, and if you can find it you start from that point and then start calculating motor loads additions from there and all other calculation factors. But if this is an old system it may not be marked anywhere, then you would start from scratch.This is a very large, heavy-industrial facility with big MVA transformers in a client-owned utility SS. They feed several 15kV SWGR which in turn feed numerous 13.8kV - 480V XFMRs
They in turn feed 480V SWGR which has feeders run to local bus bar enclosures that tap down into small dry type XMFR that feed 480-480/277V and 480-208/120V panelboard that feed small loads such as the HVAC unit.
I assume the large XFMRs and SWGR have already been calculated and I should focus on the small XFMRs to Panelboard to HVAC for short circuit cable sizing.
Correct me if I’m wrong here.