jim dungar said:If there two 120V transformer windings connected in series (winding X1-X2 and X3-X4) the only reason you would say that the voltages are subtracted from each other is to justify your 180 degree logic. Because when the discussion is 3-phase wye circuits the common statement becomes "add the voltages vectorially". How about some consistency?
No Jim,
That is the way it is. If we reference both V1 and V2 to neutral and assign zero phase angle to V1, then:
V1n = 120V @ 0
V2n = 120V @ 180
Now to obtain V12, we must measure the DIFFERENCE in potential between L1 and L2. This is fundamental in any voltage measurement.
Then V12 = V1n - V2n
V2 <----------n---------->V1
V2 ----------------------->V12
It would be more precise to say subtract vectorially.