I believe so. But I was able to thread the chase nipple into it all the way making a very tight connection.Chase nipple have straight threads aren't those street elbows designed for tapered threads?
Yup.You put the fitting on the box and inserted thru the hole into the bottom of panel?
Clever
No, it’s a listed rigid fitting.Isn't that a pressure pipe or gas fitting?
Conduit couplings have straight threads, so is there an issue if you use a chase nipple going into a coupling? Presumably with a regular conduit elbow.Replace the chase nipples with close nipple and locknuts and it's code compliant.
Right, the radius on the 3/4" elbow appears to be 2-1/4" or less, while Chapter 9 Table 2 specifies a minimum radius of 4-1/2".Are those elbows permitted to be concealed?
$7.66 at GordonThat's still a $14 fitting, at .3/4" interesting...
Good idea about using close nipples.Replace the chase nipples with close nipple and locknuts and it's code compliant.
Are those elbows permitted to be concealed?
For what it’s worth, I did run a EGC conductor. I used donut reducers because I came in through a larger KO and I wasn’t sure if these chase nipples are good for bonding so I figured running the conductor was the best bet.Conduit couplings have straight threads, so is there an issue if you use a chase nipple going into a coupling? Presumably with a regular conduit elbow.
Also, if a run is mechanically secure, and only has one thread mismatch in it, that's just a bonding issue? Which could then be take care of by running a wire type EGC?
Right, the radius on the 3/4" elbow appears to be 2-1/4" or less, while Chapter 9 Table 2 specifies a minimum radius of 4-1/2".
Cheers, Wayne
For what it’s worth, I did run a EGC conductor. I used donut reducers because I came in through a larger KO and I wasn’t sure if these chase nipples are good for bonding so I figured running the conductor was the best bet.
As far as the radius, would that apply in a listed fitting?
348.42 Couplings and Connectors. Angle connectors shall not
be concealed.
I thought that was only because they came apart to install the conductors?Yes, Have you seen those listed 90's for flex? They cannot be installed in a concealed location