My bad, you are correct. When I posted I was thinking crtemp was going to connect both cooktop and wall oven on same circuit.I disagree.
Only a single range or combination of wall & counter top units are treated as one range according to note #4. The part in red says the nameplate is the branch circuit load. There is no demand factor for a branch circuit for this, only a feeder/service load demand factor. That's the way I read it anyway.