Is this Dangerous?

Status
Not open for further replies.

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Are you guys saying the disconnect on the left should have the conductors reversed, meaning top goes where bottom ones are and vice-versa? Or the cabinet flipped around?
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Are you guys saying the disconnect on the left should have the conductors reversed, meaning top goes where bottom ones are and vice-versa? Or the cabinet flipped around?
Yes, that's the idea, although I don't think you could simply flip the cabinet. Isn't there a requirement that "ON" be "up"?
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
It seems silly to me that the next size up rule does not apply here. The difference in ampacity vs short circuit protection by the primary fuses would seem to make little difference, and the secondary fuses provide just fine overload protection.

I am far more concerned about the line vs load side disconnect issue.

-Jon
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
So, curious, would you replace the conductors or splice them in that disconnect to extend them to the correct lugs? I think I would splice them (does that make me a hack?).

I would probably look at replacing the fusible switch with a breaker, and provide properly sized conductors from the transformer secondary.
 

oldsparky52

Senior Member
I would probably look at replacing the fusible switch with a breaker, and provide properly sized conductors from the transformer secondary.
Yea, I did forget the conductors were too small. Well, I still think the most cost effective way to do it would be to use that switch, splice the load conductors so they reach the proper lugs and install (like you said) properly sized conductors from the transformer secondary.
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
Damn, I could have sworn that the 'ambient temperature correction factors' went below 21C. But the tables only get us to 399A for 500kcmil

-Jon
 