- Licensed Electrician
2020 code has a requirement for a disconnect for a fused disconnect.
They did use a lot of tape.I admit it took me a minute to see what was wrong, I was looking way to hard. I must have been subconsciously mesmerized by the tape job![]()
The fuses aren't "at the secondary." They're downstream from the secondary.The fuses are OCP so I don't see how 240.21 (C) would apply at all.
Yes, that's the idea, although I don't think you could simply flip the cabinet. Isn't there a requirement that "ON" be "up"?Are you guys saying the disconnect on the left should have the conductors reversed, meaning top goes where bottom ones are and vice-versa? Or the cabinet flipped around?
"next size up" rule only would apply to the load side of the fuses hereThe fuses are OCP so I don't see how 240.21 (C) would apply at all.
So, curious, would you replace the conductors or splice them in that disconnect to extend them to the correct lugs? I think I would splice them (does that make me a hack?).
Yea, I did forget the conductors were too small. Well, I still think the most cost effective way to do it would be to use that switch, splice the load conductors so they reach the proper lugs and install (like you said) properly sized conductors from the transformer secondary.I would probably look at replacing the fusible switch with a breaker, and provide properly sized conductors from the transformer secondary.
If the load allows it, could they replace the 400-amp fuses with 350-amp fuses and the wire size be okay?The fuses aren't "at the secondary." They're downstream from the secondary.
Me too!I admit it took me a minute to see what was wrong, I was looking way to hard. I must have been subconsciously mesmerized by the tape job![]()
This is one of those convoluted code requirements that makes zero sense but the issue is the conductors from the transformer to the fuses.If the load allows it, could they replace the 400-amp fuses with 350-amp fuses and the wire size be okay?
NMThe fuses aren't "at the secondary." They're downstream from the secondary.
Just turn the AC to less than 68FIf the load allows it, could they replace the 400-amp fuses with 350-amp fuses and the wire size be okay?
More than...Just turn the AC to less than 68F
Less than 68F...to increase conductor ampacity.More than...
?Damn, I could have sworn that the 'ambient temperature correction factors' went below 21C. But the tables only get us to 399A for 500kcmil
-Jon