From another thread, and a pet peeve of mine, I bring you a poll....

Is this device grounded?

attachment.php



If it is not grounded - under what conditions could it be grounded?
If it is grounded - state a code ref...
If it is not grounded - state a code ref...
 
404.9(B)(1) doesn't ask for anything more than metal screws. I say the metal yoke is grounded.
 
But, but, but....

'What about 404.9(B)1? It's 'mounted' to a metal box with metal screws???? :confused:'

But, but, but....

'It's easier this way.... and the code says....'

But, but, but....

'What if the screws were tighter?'


IMPO it's really not "mounted" - to anything...
 
What is the device yoke "mounted" to?

The words "firmly secured" are clearly describing the word "mounting" - nothing in the picture is "firmly secured" to anything, and if it were - it would be secured to sheet-rock - not the metal box...
I'll agree that the diagram shows an incomplete installation.
 
Here's the Code
2008 NEC

404.9 Provisions for General-Use Snap Switches.

(B) Grounding.
Snap switches, including dimmer and similar control switches, shall be connected to an equipment grounding conductor and shall provide a means to connect metal faceplates to the equipment grounding conductor, whether or not a metal faceplate is installed. Snap switches shall be considered to be part of an effective ground-fault current path if either of the following conditions is met:
(1) The switch is mounted with metal screws to a metal box or metal cover that is connected to an equipment grounding conductor or to a nonmetallic box with integral means for connecting to an equipment grounding conductor.
 