Is this device grounded?

Learn the NEC with Mike Holt now!

Is this device grounded?


  • Total voters
    97
Status
Not open for further replies.
How does this install situation fit the condition in 404.9(B)1?????


IMPO this portion of the code should be more clear - but here we are.... :roll:
It fits 'cause the passage doesn't say "tight", or something like that, to describe the state of the screws.
 
Probably a stupid question---> I only use P&SL devices so I don't know about other brands but isn't this part of the reason they switched to the little wire screw retaining clips as opposed to the little piece of oil board?
 
Here's the Code
2008 NEC

404.9 Provisions for General-Use Snap Switches.

(B) Grounding.
Snap switches, including dimmer and similar control switches, shall be connected to an equipment grounding conductor and shall provide a means to connect metal faceplates to the equipment grounding conductor, whether or not a metal faceplate is installed. Snap switches shall be considered to be part of an effective ground-fault current path if either of the following conditions is met:
(1) The switch is mounted with metal screws to a metal box or metal
cover that is connected to an equipment grounding conductor or to a nonmetallic box with integral means for connecting to an equipment grounding conductor.
If this were a surface mounted box with even semi-snug connections I would say it fits the code. In this case the switch can not be considered "Mounted" to anything, and if the screws were tight it would be "mounted' to the sheetrock - not the box....
 
Probably a stupid question---> I only use P&SL devices so I don't know about other brands but isn't this part of the reason they switched to the little wire screw retaining clips as opposed to the little piece of oil board?
That is a self-grounding device.... ;)
 
There is nothing permanent about a intermittent path.

Would you view a foot lug connected loosely to an enclosure as meeting 250.4(A)(5)
Well, the lug doesn't have the equivalent of the mounting instructions implied in 404.9(B)(1).

One way the language of 404.9(B)(1) could be improved would be by saying something like "firmly mounted" in the condition of (1).

But as is, 404.9(B)(1) doesn't exclude loose mounting, IMHO.
 
If this were a surface mounted box with even semi-snug connections I would say it fits the code. In this case the switch can not be considered "Mounted" to anything, and if the screws were tight it would be "mounted' to the sheetrock - not the box....
Mounting, IMO, is not exclusively "mounting directly to the box". I just don't see that in the language.
 
There is nothing permanent about a intermittent path.
Now, if the Poll Question was: "As illustrated, is there electrical continutiy that is reliable between the dimmer yoke and the box?" I would answer no.
 
One way the language of 404.9(B)(1) could be improved would be by saying something like "firmly mounted" in the condition of (1).

But as is, 404.9(B)(1) doesn't exclude loose mounting, IMHO.
I agree - but 250.4(A)5 does...

Mounting, IMO, is not exclusively "mounting directly to the box". I just don't see that in the language.
In the case of flush mounted boxes - in most cases a mud ring only acts as a toggle for mounting to the gypsum surface... It is and could not be mounted to the box at all - unless the ring were proud of the rock surface. If the yoke could touch the box - I would say it were "mounted" "to the metal box" it "with metal screws" and meet the condition in 404.(B)1 - otherwise it needs an EGC - IMO.

Now, if the Poll Question was: "As illustrated, is there electrical continutiy that is reliable between the dimmer yoke and the box?" I would answer no.
The question was is this device grounded? "Grounded" has a definition in 100, and in this case is a connection between the device yoke and the box - not the screws used to do so.
 
Not that my opinion counts, but that is the answer I have been looking for as I have read the posts on this thread. Thank you sir.
Oh you count.... Just as much as the rest of us. But the question was what it was - is it grounded or not? Only two answers: yes or no? No tricks or qualifiers...
 
Oh you count.... Just as much as the rest of us. But the question was what it was - is it grounded or not? Only two answers: yes or no? No tricks or qualifiers...

Okay, then yes it it is grounded per 404.9(B)(1). As stated it says metal screws and that is what is shown. I do not like it, but it says what it says. Nothing about tight or in contact. Implied: yes, Stated :no.
 
One way the language of 404.9(B)(1) could be improved would be by saying something like "firmly mounted" in the condition of (1).

But as is, 404.9(B)(1) doesn't exclude loose mounting, IMHO.

I think it is generally expected that an electrical connection not be loose and that we are not always specifically told a connection must be tight.
 
I think it is generally expected that an electrical connection not be loose and that we are not always specifically told a connection must be tight.
I submit that the real issue with the OP diagram is that the mounting is loose. As such it doesn't meet the requirements in 110.13(A). Devices are Equipment.

When this dimmer is firmly against the wall, then the screws are making a connection tight enough, evidently, as that's what 404.9(B)(1) and 404.9(B) seem to say.
 
My two zincs...

I agree - but 250.4(A)5 does...

As does 404.10(B).

404.9(B)(1) does not say the yoke has to make physical contact with the metal box or grounded box ring. The switch in the picture is mounted to a grounded metal cover with metal screws, thus it satisfies that section.

Loose screws do not make for an effective ground path, so I say the switch is not grounded.
 
Okay, then yes it it is grounded per404.9(B)(1). As stated it says metal screws and that is what is shown. I do not like it, but it says what it says. Nothing about tight or in contact. Implied: yes, Stated :no.
It says mounted to a metal box - it isn't... If it were tight - it would be mounted to the gyp board... ;) If we want to get technical - it is at minimum mounted to the ring - not the "box". (And it is not mounted to a cover either...)
 
It says mounted to a metal box - it isn't... If it were tight - it would be mounted to the gyp board... ;) If we want to get technical - it is at minimum mounted to the ring - not the "box". (And it is not mounted to a cover either...)
May I suggest replacing the box / plaster ring with a simple single gang wall case? That side steps this and keeps the focus on your initial question.
 
May I suggest replacing the box / plaster ring with a simple single gang wall case? That side steps this and keeps the focus on your initial question.

Alright - It is exactly the same... Still not mounted to the box... And... Not grounded!