jaylectricity
Senior Member
- Location
- Massachusetts
- Occupation
- licensed journeyman electrician
Has anybody plugged one of these into it yet? :grin:

Hence my point earlier:
Wow. You're hot tonight. Nice graphic.Alright - It is exactly the same... Still not mounted to the box... And... Not grounded!
![]()
Sure.....Wow. You're hot tonight. Nice graphic.
So complete the installation with the screws snugged down, and with the box set back as shown.
IMO, this is the heart of the question. A realistic, common, as-installed in the real world assembly. When the device screws are snugged down, is the heat sink / yoke bonded to the EGC?
Sure.....
![]()
Still not grounded!
Not secured to the box...
____________________________________________________________
Submitter: Rod Belisle, NECA-IBEW Electrical Training Center
Comment on Proposal No: 9-95
Recommendation: “Accept” to read as follows:
Revise 404.9(B)(1) as follows:
The switch is mounted with metal screws to a surface-mounted metal box
with at least one of the insulating washers removed or to a nonmetallic box
with integral means for grounding devices.
Substantiation:
The requirements in 404.9(B) state that a switch shall be
“effectively grounded”.
The definition of effectively grounded in Article 100, states that it shall be
sufficiently low impedance and have sufficient current carrying capacity to
prevent the buildup of voltages that may result…
It is not accurate to state that a switch mounted on a non-conductive surface,
secured to a metal box that is recessed _”, therefore not touching the switch,
meets the requirements of “Effectively grounded”.
The CMP substantiated it’s vote by stating that the requirement is not the
same as the requirement for receptacles, but the terminology used in 404.9(B)
does not differentiate for the code user.
The use of the term “effectively grounded” needs to mean the same thing as
used throughout the NEC, as it is described in Article 100.
Panel Meeting Action: Reject
Panel Statement:
The proposed requirement is the same as 250.146(A) for
receptacles and as such is excessive for snap switches that do not form an
element in the extension of a circuit beyond the fixed wiring of a building
or structure. This has been the consistent position of CMP 9 on this point for
at least 70 years, and there has not been adequate technical substantiation
presented to justify this change.
Number Eligible to Vote: 11
Ballot Results: Affirmative: 11
Actually they disagreed with the writer of that particular revision... Not "ME" specifically...The CMP diagrees with you :
9-107 Log #4538 NEC-P09 Final Action: Reject (404.9(B))
Submitter: Phil Simmons, Simmons Electrical Services Recommendation: Revise the existing text of the 2008 NEC as follows:
(B) Provision for Grounding. Snap switches, including dimmer and similar control switches, shall be connected to an equipment grounding conductor and shall provide a means to connect metal faceplates to the equipment grounding conductor, whether or not a metal faceplate is installed. Snap switches shall be considered to be part of an effective ground-fault current path if either of the following conditions is met:
(1) The switch is mounted with metal screws to a metal box or metal cover that is connected to an equipment grounding conductor or to a nonmetallic box with integral means for connecting to an equipment grounding conductor.
(2) An equipment grounding conductor or equipment bonding jumper is connected to an equipment grounding termination of the snap switch. Exception to (B): Where no means exists within the snap-switch enclosure for connecting to the equipment grounding conductor or where the wiring method does not include or provide an equipment grounding conductor, a snap switch without a connection to an equipment grounding conductor shall be permitted for replacement purposes only. A snap switch wired under the provisions of this exception and located within reach of earth, grade, conducting floors, or other conducting surfaces shall be provided with a faceplate of nonconducting, noncombustible material or shall be protected by a ground-fault circuit interrupter. Substantiation: This proposal intends to move the installation requirements for grounding switches to Article 250 under the jurisdiction of CMP-5. The construction requirements are appropriate to remain in Article 410.
Panel Meeting Action: Reject Panel Statement: The grounding provisions for snap switches should remain in Article 404. These devices are self-contained and, unlike receptacles, they do not provide a portal for a quasi branch-circuit extension beyond the device in the form of a cord. These requirements have been in this location for many code cycles, and users are accustomed to finding them in their current location. Note also the discussion and panel actions in this cycle regarding Proposals 9-110 and 9-111 for examples of where grounding rules become complicated by the design of some current styles of snap switches with novel internal constructions.
Number Eligible to Vote: 12 Ballot Results: Affirmative: 12
What is the device yoke "mounted" to?
The words "firmly secured" are clearly describing the word "mounting" - nothing in the picture is "firmly secured" to anything, and if it were - it would be secured to sheet-rock - not the metal box...
No it does not - no EGC.... Why this thread???? Not long ago I found a bunch little green wires sitting in the trash bucket... Another thread reminded me of that incident....Does this dimmer have a green wire ? If yes then grounded asuming you use it. If no green wire or grd screw the i say not grounded. Can't vote without knowing that.
If I go with the wording of either the CMP statement he, or the one I posted then there is no purpose for having a green wire, a ground screw or ever grounding a switch EVER AGAIN! EVER!!!! Because seriously - it that is an acceptable method of grounding the yoke, then it can also be assumed it is just as an effective ground fault current path for any plate attached to said yoke..... So - I have changed my mind.... I have learned that the CMP involved with switches has no given a flying hoot about grounding of switches for over 70 years - and nor should I.....The CMP diagrees with you :
These devices are self-contained and, unlike receptacles, they do not provide a portal for a quasi branch-circuit extension beyond the device......
switches ~ do not form an
element in the extension of a circuit beyond the fixed wiring of a building
or structure. This has been the consistent position of CMP 9 on this point for
at least 70 years