I'm involved with a campus of several buildings all fed from a switchboard outside near a central parking lot.
Are feeders from the switchboard into each building considered service entrance conductors/does the maximum 6 disconnects rule come in to play here?
The code seems to make it clear that only the conductors from the utility are service conductors, but I could see an argument made to follow the service disconnect rules for each building.