I know for certain that I wouldn't buy anything called an inverter that clearly did not contain an inverter.
So all of your MWBCs have only two wires, right?As for the phase leg used on single Phase I Have learned to ignore it.
So all of your MWBCs have only two wires, right?
I don't see anything inherently unsafe in the idea. People have been doing it for a long time without the box.
I guess I didn't think of sustain as having more then one definition, my bad there, maybe, so I guess replace sustain in my statement there with maintain and hopefully that gets what I meant to say across. GD otherwise explained it in further detail.This is like comparing apples to oranges. In manufactured appliances and equipment if designed for a higher voltage it will pull less current than one designed for a lower voltage.
We where talking about using a higher voltage or double the voltage on something that was designed for a lower voltage and so the amps. would be more.
The motor example was not a good example I shouldn't have used it.
Please explain I don't understand.
I have to say I've seen a lot of things with 50 amp plug on them, that did not require a 50 amp circuit. But outside of some welders not one of them ever came from the manufacturer with a cord cap either from what I can recall.Anyone ever seen a pressure washer with a 50 AMP plug on it (maybe but it's not normal).
I am sure the yellow cords have UL stickers on them. That takes care of the whole thing, right? :angel:
Steambrite has a lousy product for saleCame across this. Not sure if its a bright idea or a disaster waiting to happen. What do you guys think?
The receptacle in the OP doesn't have a neutral terminal, had it been a 14-50 instead of a 6-50 receptacle that would be a bigger concern. Otherwise don't connect the neutrals in the two supply cords together and you do not create any neutral issues. Not trying to make excuses to encourage the use of this product - just telling you what I see.does anybody think there is a problem with the paralleling of the neutrals that this thing will create? I'm sure they connected the neutrals from each cord together on the 50 amp receptacle.
So please tell me that this contraption is UL listed??? I very much doubt it, it has so many code violations all over it that UL would just :lol:
does anybody think there is a problem with the paralleling of the neutrals that this thing will create? I'm sure they connected the neutrals from each cord together on the 50 amp receptacle.
So please tell me that this contraption is UL listed??? I very much doubt it, it has so many code violations all over it that UL would just :lol:
The receptacle in the OP doesn't have a neutral terminal, had it been a 14-50 instead of a 6-50 receptacle that would be a bigger concern. Otherwise don't connect the neutrals in the two supply cords together and you do not create any neutral issues. Not trying to make excuses to encourage the use of this product - just telling you what I see.
You eliminate the neutral from an existing circuit from being introduced to another circuit, you don't need a neutral for the load you are trying to supply, so you resolve one possible problem by not connecting the neutrals in the supply cords together, there are still other problems introduced by such a contraption.Don't connect the neutrals.
So won't that really create other problems.
You eliminate the neutral from an existing circuit from being introduced to another circuit, you don't need a neutral for the load you are trying to supply, so you resolve one possible problem by not connecting the neutrals in the supply cords together, there are still other problems introduced by such a contraption.
I am sorry to be thick here, but aren't you stuck with neutral problems even if the neutrals are separated? Isn't current going directly from one hot leg to the other instead of back through the neutral(s), making GFCIs trip?Don't connect the neutrals. So won't that really create other problems.
The receptacle in the OP doesn't have a neutral terminal, had it been a 14-50 instead of a 6-50 receptacle that would be a bigger concern. Otherwise don't connect the neutrals in the two supply cords together and you do not create any neutral issues. Not trying to make excuses to encourage the use of this product - just telling you what I see.
Very good, now how many permits do you get to look at such a device, or much of anything that plugs in but nothing else is associated with the permit? I think the bigger question here is is it safe. It could be argued the branch circuit(s) end at the outlet (receptacle) and NEC doesn't apply to what is plugged in. What maybe could be argued is the appliance supplied by the 240 volt receptacle isn't fed with code compliant branch circuit wiring/methods, and come up with multiple things from that perspective that are in violation.I say unsafe and not code compliant.
Branch Circuit, Multiwire. A branch circuit that consists
of two or more ungrounded conductors that have a voltage
between them, and a grounded conductor that has equal
voltage between it and each ungrounded conductor of the
circuit and that is connected to the neutral or grounded
conductor of the system.
210.4 Multiwire Branch Circuits.
(A) General. Branch circuits recognized by this article shall
be permitted as multiwire circuits. A multiwire circuit shall be
permitted to be considered as multiple circuits. All conductors
of a multiwire branch circuit shall originate from the same
panelboard or similar distribution equipment.
(B) Disconnecting Means. Each multiwire branch circuit
shall be provided with a means that will simultaneously
disconnect all ungrounded conductors at the point where
the branch circuit originates.
If you are powering a straight 240 volt load you don't need a neutral at all to make that load work, so why should you have a problem with the neutral itself as long as you don't tie the two together from the supply cords making a possible alternate path for the premises wiring neutral(s)?I am sorry to be thick here, but aren't you stuck with neutral problems even if the neutrals are separated? Isn't current going directly from one hot leg to the other instead of back through the neutral(s), making GFCIs trip?