Re: Isolation of neutral at Sub Panels
eagle: You have noticed that my opinion is not well accepted
However I stand by my interpretation for the following reasons; The absence of the term "sub-panel" is glaringly apparent in all editions of the NEC.
The NEC does not contain a section that states "the neutral and ground shall be separated in any panels". If so please tell me.
This procedure is the creative method by someone, to stop current flow on conduits.
Section 250.24(5). Does not apply to a panel, the intent is to insure the equipment ground and neutral are separated at the utilization equipment.
Preventing objectionable current from appearing on conduit or other conductors, can be done by any of the methods as described in 250.6(B). When metal conduit is used as an equipment ground, there is no choice but to separate the neutral and ground in the panel.
The reason that the term "sub-panel" does not, and never will appear in the NEC, is due to the technical incorrectness of the term.
When you have six panels, with mains, grouped on a wall with a 30 ft. long gutter, supplying the service conductors to each one, do you consider the panels to be service panels? Of course they are.
Now should the panels be replaced with main circuits breakers and feeding six panels in apartments, does this change the logic of the electrical application?
The service mains have to be grouped, there is nothing wrong with separating the panels.
I understand that some individuals remove the neutral to ground jumper ribbon in transformers to prevent parallel current when the neutral/ground is bonded in the first switch.
This is a dangerous method, and should never be done. This is the same thinking when it was decided to run a fourth wire to a place that only needed three.