 - Chapel Hill, NC
 - Retired Electrical Contractor
Okay, what am I missing?  Why are we only looking at 49kw.  Doesn't each phase have 2 loads of 49kw?
So if there were only 2 49 kw loads both going to phases A and B - loads are sp 480V--what is the load on A or B?
190104-1031 EST
Dennis Alwon:
Your question is not clear.
What do you mean by phase A or B? What does load on A or B mean.
Each phase will has to be defined by two points. Your phases A and B are not defined.
A load has to be defined relative to the two points it connects to.
Te currents are not in phase so you can't just add them arithmetically.I've been drawing out the circuits trying to see where the change in the load amps happens. I am very familiar with the 1.73 factor for three phase power. I'm seeing the B phase node at 102 + 102 = 204.
I agree. Assuming the loads are all unity power factor.Been too many years since college & computers have ruined me..
My computer, if it can be trusted, shows the load to be 178 amps, next standard size fuse would be 200 amps.
I'll let one of the young 'uns show you the math(.and check me)![]()
Strathead explained it well, What I was saying was given the same example but with 2 49kw loads connected to Phase A and Phase B only. Phase C is not connected at all... What would the reading be on Phase A and Phase B--
I still really don't know what your question is.Strathead explained it well, What I was saying was given the same example but with 2 49kw loads connected to Phase A and Phase B only. Phase C is not connected at all... What would the reading be on Phase A and Phase B--
190104-1848 EST
Dennis Alwon:
A three phase transformer has nothing to do with your question. Two output terminals of a three phase transformer constitutes a single phase source. It is the same as two terminals of a battery in a DC circuit, or two terminals on a doorbell transformer.
Clamp your meter around the lead going to terminal A and the reading is 10.4 A . Same for terminal B.
Clamp your meter around one lead to one 2.49 kW load and the reading is 5.2 A.
Do the experiment in some fashion on your bench.
Well that is what I originally thought and with all the chatter I got confused. In the original post there is a 3 phase delta and for some reason you don't add the loads on one feeder conductor. Do you see what I am saying?
What convention are you using to relate the Phase letter to the wire designator?Strathead explained it well, What I was saying was given the same example but with 2 49kw loads connected to Phase A and Phase B only. Phase C is not connected at all... What would the reading be on Phase A and Phase B--