With 300 watt lamps....I still have some active K&T in the attic of my 1925 home, it is buried in blown in insulation and I sleep just fine. It feeds some ceiling lights.
With 300 watt lamps....I still have some active K&T in the attic of my 1925 home, it is buried in blown in insulation and I sleep just fine. It feeds some ceiling lights.
I would never sign anything stating there is none in use - unless I did run all new circuits in the place and know nothing old was reconnected.
Does anyone know when it became a violation to cover knob and tube in attics with insulation?
I have never seen a neutral shared with more than one circuit on any of the K&T that I have worked on. As far as the size of the fuse being increased, that applies to any wiring method.I think the main trouble with K&T is when it's installed in a home that still has a fuse panel and that fuse panel has the ability to house 30amp fuses AND the neutrals are all shared so the full load of two circuits may be carried on one neutral for a time.
And duplex lamp adapters.With 300 watt lamps....
Until you have verified what is concealed you don't have a clue. If owner wished to remove all wall and ceiling coverings so it is easy to verify I will not state it is K & T free, even with quite a bit of newer wiring present - they often do tap at least a portion of an old circuit onto a newer circuit.Yeah, well, as an electrician I'd assume you'd know for sure whether or not there was anything K&T connected.
And duplex lamp adapters.
Until you have verified what is concealed you don't have a clue. If owner wished to remove all wall and ceiling coverings so it is easy to verify I will not state it is K & T free, even with quite a bit of newer wiring present - they often do tap at least a portion of an old circuit onto a newer circuit.
The 2 Button switch that still works!
I have never seen a neutral shared with more than one circuit on any of the K&T that I have worked on. As far as the size of the fuse being increased, that applies to any wiring method.
Also if there is no insulation the K&T is a "free air" installation and the 60°C ampacity of #14 copper is 25 amps in free air, the 75°C ampacity is 30 amps, so even with a 30 amp fuse, there is not a serious hazard as long as the K&T is not in insulation.
Really no issue with a 30 amp fuse. What planet are you on. K&T us not a free air wiring system.
I had a friend with a apartment bldg with N&T, almost burned to the ground. The renter placed 30 amp fuses in the Edison base holders. cooked the wiring and started a fire one winter. Had a heater plugged in a 14 gauge wire.
1987: NEC- 324.4: "Concealed knob and tube wiring shall not be used in the hollow spaces of walls, ceilings, or attics when such spaces are insulated by loose or rolled insulating material."
If the 14 AWG conductor is not in contact with other materials besides the porcelain knobs and tubes - what is going to start a fire? You could load it until the insulation is burned off which wold likely take well over 30 amps to do and it will still be left hanging there on the porcelain knobs and tubes, it needs to have something combustible in close enough proximity to start a fire.
Thanks, so prior to 1987, it would have been legal to blow insulation over K & T? I'm sure in this case, it was done pre 1987 so therefore, it would be acceptable as is.
Thanks, so prior to 1987, it would have been legal to blow insulation over K & T?
Don't know how to interpret what was mentioned there. Could be he just happened to find that section in 1987 NEC or it could be new text for that year.
Thanks, that is what I wanted verification of.The original 324.4 of 1987 has indeed become the 394.12 of 2014.
Thanks, that is what I wanted verification of.
This does complicate things though. Technically insulation installed enveloping k &T wiring before 1987 is code compliant.
It seems it would make things more questionable during a K & T check because barring personal knowledge from the h.o., how would one be certain when the attic was insulated with the cellulose?
Makes we really wonder why anyone in a cold climate on the east would keep K&T