If the voltage is not induced...I have a major problem ~ the installation was not done properly. I can see that happening as one of the guys (who worked on the second floor where the smokes start) tightened the clamps a bit too tight...I pray he wasn't as zealous with the staples.Pierre C Belarge said:Celtic
Having an induced voltage for this type of installation is most likely a common installation...so I believe you can rule out the induced voltage as an issue.
Done ....twice.Pierre C Belarge said:1. Check the continuity of all of the conductors between units (which I believe you already have done). Make sure there is an open in the circuit as well by opening the conductors...you could have a dead short in the signaling conductor.
Buying new units was not an option this weekend - supply house is closed.Pierre C Belarge said:2. As Marc has stated, use a 9volt battery and see if you can get a response from any of the units. Try doing this from several the units, not just from one location.
If this does not work, try this: buy 3 new units. rig them up on a table or the floor and wire them... then test them with battery and actual 120v power...see if they work. If they do, and the ones in the ceiling do not, maybe you have a few defective units (it happens) and they need to be replaced.
All the units and tails are "down" at this point...a 9v test is the first item on today's (yes, today) list. I'm basically booked Monday - Thursday...and the people move in on the 29th of Sept. ...not many days left.
Nope...not done ....but will doPierre C Belarge said:3. Check the batteries in the units (you may have done this already).
Pierre C Belarge said:Good luck, I know I would have already changed out the units by now myself...I do not drink as much JOLT as you do, and have much less patience with this kind of issue. :wink:
When the HO and GC are in/out all today, one must "appear" to be patient - even though we dread the inevitable...... I just hope my worst fear does not appear.