appliances rated at 5.4 Kilowatt @ 120/240 and 4.8 kilowatt @ 120/240 what is the amp rating for each I say 60 amps for the 5.4 and 50 amps for the 4.8 please help me out global
This is an example of the reason learning simple Ohms Law is important to everyday electricians. Without the knowledge, they are mostly "shooting in the dark".
The excuse that no one has taught them is no longer acceptable, as this information is readily available at your fingertips.
I can't come up with any calculation method that arrives at those numbers. Care to share how you did it? If you are willing, then perhaps we may be able to help you see where you have gotten it wrong.. . . I say 60 amps for the 5.4 and 50 amps for the 4.8 please help me out global
Sorry, but you are. You should be dividing by 240, not by 120.Maybe I'm wrong, but the answer is 45 and 40
Maybe I'm wrong, but the answer is 45 and 40
5.400 watts divided by 120 volts = 45 amps breaker
4.800 watts divided by 120 volts = 40 amps breaker![]()
Not true. The load was described as 120/240 volt. That must necessarily mean that the breaker is a two-pole, and that 240 volts is available to the load. Therefore, you divide the VA by 240, not by 120.x by 120 volts because at the breaker pole 120 volts exist, not 220
No...240 exists line to line ... a 60 amp breaker will supply 14.4 kva at 100% or 11.5 kva at 80%.45 amp and 40 amp = 56.25 amps and 50 amps at 125 percent, so a 60 and 50 amp breaker should be right.
x by 120 volts because at the breaker pole 120 volts exist, not 220
60 amp two pole breaker and a 50 amp two pole breaker![]()
45 amp and 40 amp = 56.25 amps and 50 amps at 125 percent, so a 60 and 50 amp breaker should be right.
50 amps at 125 percent,
By the way David, welcome to the forum.:smile:
Not true. The load was described as 120/240 volt. That must necessarily mean that the breaker is a two-pole, and that 240 volts is available to the load. Therefore, you divide the VA by 240, not by 120.
Very sharp... I'll let my other thoughts GO! :grin:No...240 exists line to line ... a 60 amp breaker will supply 14.4 kva at 100% or 11.5 kva at 80%.
It's being well moderated!!! :grin:Boy this is a rough first day.
Yes, that thought struck me too when I read the OP.Charlie covered the calculation error but beyond that from the information provided there is no way to determine the breaker size.
We also are stuck assuming a power factor of 1 without more info.
And, at 5.4kW, is it beyond the bounds of possibility that it could be a three-phase load?