And, at 5.4kW, is it beyond the bounds of possibility that it could be a three-phase load?
I thought so too.I thought, and I could be wrong, that 120/240 ruled that out.
And, at 5.4kW, is it beyond the bounds of possibility that it could be a three-phase load?
I thought so too.I thought, and I could be wrong, that 120/240 ruled that out.
The OP says: "appliances rated at 5.4 Kilowatt @ 120/240"
I thought so too.
The OP says: "appliances rated at 5.4 Kilowatt @ 120/240"
Wouldn't 120/240 , particularly in the US, normally refer to the supply rather than the appliance?
Bottom line - there just isn't enough information in the OP to give a definitive answer.
120/240V means you have the option to connect the equipment to either 120V or 240V.
#1 @ 120V = 45A load with min 50A breaker.
#1 @ 240V = 22.5A load with min 25A breaker.
#2 @ 120V = 40A load with min 40A breaker. (larger is suggested)
#2 @ 240V = 20A load with min 20A breaker. (larger is suggested)
That would mean it uses both, just like an electric dryer or range is rated 120/240.
Actually I will change that to it could mean either, we need more info.
Good to see that at least three of us now agree on that point.Plain and simple, there is not enough information to provide a definitive answer.
Again we can not determine the correct OCPD with the information provided.
I dug thru the UL web site about nameplate markings and found this.That would mean it uses both, just like an electric dryer or range is rated 120/240.
Some equipment is marked for use on more than one voltage. Individual voltage ratings may be a single value or a range of values as indicated above, with each of the multiple ratings separated from the others by a slash (e.g., ?208/240? or ?220?240/440?480?) or by a separate line or column in a tabulation of ratings.
Since no indication of '3W' or '3ph, 4W' was indicated with the nameplate I'll assume the equipment can be connected to 120V or 240V. And if connected at 240V it does not require a neutral connection.Some equipment showing two voltage ratings may be designated to have both voltages supplied from the same supply circuit. In such cases, the rating indicates the number of wires needed in the supply circuit (e.g., ?120/240 V, 3W? or ?120/240 V, 3ph, 4W?) or the number of wires will be indicated clearly on the wiring diagram attached to the unit.
No, but we can determine the minimum, which may or may not be correct. Or at the very least answer how many amps for the connected load.Again we can not determine the correct OCPD with the information provided.
Is that an acceptance of defeat or do you simply mean 'agree to disagree'?That's just too diplomatic. :wink:
appliances rated at 5.4 Kilowatt @ 120/240 and 4.8 kilowatt @ 120/240
No, but we can determine the minimum, which may or may not be correct.
Ah, Ohm's Law and Watt's Law. :wink:I can agree on E = I * R. But I would argue to include P = E * I.
Ah, Ohm's Law and Watt's Law. :wink:
It's single phase. Just like that neutral in that powerpoint presentation was a neutral and not a ground. Now I'm beginning to understand why you thought it was a ground.The OP says: "appliances rated at 5.4 Kilowatt @ 120/240"
Wouldn't 120/240 , particularly in the US, normally refer to the supply rather than the appliance?
Bottom line - there just isn't enough information in the OP to give a definitive answer.