Not it's not compliant, and that's because you don't have working space. You need floor to 6.5 feet above the floor right in front of the panel, and clearly the countertop is in that space.I've never seen one installed right above the countertop. Is it compliant? There's a workspace issue at minimum.
And the PT leads are not connected in an approved manner.Looks like there's 2 sets of CT's ??
JAP>
And the PT leads are not connected in an approved manner.
I was wondering that myself. I have no clue.What are the CTs for?
Is that near Tampa? Looks like at least some plumbing may have been done un-permitted. They didn't want to spend the money on electrical. Used it on all that tacky tile.
I have never seen a panel in that shape... It seems like they flipped the guts 90° but then they would have to modify the cover.... Maybe just an illusion.
Agree, not compliant
Is that near Tampa? Looks like at least some plumbing may have been done un-permitted. They didn't want to spend the money on electrical. Used it on all that tacky tile.
Not it's not compliant, and that's because you don't have working space. You need floor to 6.5 feet above the floor right in front of the panel, and clearly the countertop is in that space.
At least the cover looks like it fits correctly instead of the usual half covered.
What are the CTs for?