Kitchen GFCI

Jw0307

Member
Location
California
Occupation
Electrician
Would a receptacle in a upper cabinet of a kitchen for a microwave need a GFCI? The outlet is with in 6’ of the sink but it is not servicing the counter top and it’s not along the counter top
 
Is the 6' a straight line or the path a power cord would have to take?










is
No. There is a upper cabinet specifically for the microwave above the counter and the outlet is inside of that section
Is the 6' a straight line or the path a power cord would have to take?










is

Is the 6' a straight line or the path a power cord would have to take?










is
No. The upper cabinet is specifically for the microwave above the counter and the receptacle is placed inside of that section. If that makes sense
 
No. There is a upper cabinet specifically for the microwave above the counter and the outlet is inside of that section



No. The upper cabinet is specifically for the microwave above the counter and the receptacle is placed inside of that section. If that makes sense
Is there a door in front of the microwave?
For the purposes of this section, when determining distance from receptacles the distance shall be measured as the shortest path the cord of an appliance connected to the receptacle would follow without piercing a floor, wall, ceiling, or fixed barrier, or passing through a door, doorway, or window.
 
I would think that, if a cabinet door qualifies as a door, then an open cabinet front would qualify as a doorway.
I wouldn't and there was never an intent for a cabinet door to count for this measurement, that is why that language is no longer in the code. Removing the door language made any receptacle under the sink cabinet subject to the GFCI rules. There was extensive debate after the 2017 was published and in the 2020 the language was changed to.
For the purposes of this section, when determining the distance from receptacles the distance shall be measured as the shortest path the supply cord of an appliance connected to the receptacle would follow without piercing a floor, wall, ceiling, or fixed barrier, or the shortest path without passing through a window.
 
That's pretty darned close, and it's the appliance, too, not just the receptacle.

Can you feed it through the GFCI receptacle below it?
 
That's pretty darned close, and it's the appliance, too, not just the receptacle.

Can you feed it through the GFCI receptacle below it?
How the previous Forman had it ran was based off the plans as that plug is the second small appliance circuit and it’s dedicated. If you mean by plugging micro into GFCI below then they would need to cut the bottom for the cord to go thru which they do not want to do
 
How the previous Forman had it ran was based off the plans as that plug is the second small appliance circuit and it’s dedicated. If you mean by plugging micro into GFCI below then they would need to cut the bottom for the cord to go thru which they do not want to do
No, I meant the two receptacles on one circuit. Your way would need a second GFCI.
 
I assume you mean the 2017 NEC as there is not 2019 NEC.
210.8(A)(7) in the 2017 will required GFCI protection for this receptacle because it is within 6' of the sink.
OP has the location listed as "California" so he is correct saying it's "going off of 2019 code", but you are also correct because the 2019 CA Electrical Code is based off of the 2017 NEC. I agree with your interpretation and if I was the inspector for this job, I would have called it out too.
 
The receptacle is required to be AFCI protected so why not just change the breaker to a DF?

We stopped using GFCI receptacles in the kitchen and anywhere else GFCI and AFCI is required. DF breakers are less expensive than and AFCI breaker and a GFCI receptacle. Labor is less not having to install a GFCI receptacle. Much easier to guide homeowner through resetting a breaker than trying to have them figure out which device is tripped.
 