Can kitchen island receptacles be mounted in the toe space of the cabinets?
I think it is.Is it not a Code violation to mount receptacles there. . . .
I think it is.But I will mention that this debate has taken place before, and that others have disagreed with this opinion.
Take another look at 210.52(C)(5) and its exception. They tell us where "receptacles" are to be mounted. But they do not limit that instruction to "the required minimum number of receptacles." So I infer that if you put a receptacle on an island or peninsula, it must be located where 210.52(C)(5) tells us to locate it, even if it is an "extra" one.
I think it is.But I will mention that this debate has taken place before, and that others have disagreed with this opinion.
Take another look at 210.52(C)(5) and its exception. They tell us where "receptacles" are to be mounted. But they do not limit that instruction to "the required minimum number of receptacles." So I infer that if you put a receptacle on an island or peninsula, it must be located where 210.52(C)(5) tells us to locate it, even if it is an "extra" one.
I think it is.But I will mention that this debate has taken place before, and that others have disagreed with this opinion.
Take another look at 210.52(C)(5) and its exception. They tell us where "receptacles" are to be mounted. But they do not limit that instruction to "the required minimum number of receptacles." So I infer that if you put a receptacle on an island or peninsula, it must be located where 210.52(C)(5) tells us to locate it, even if it is an "extra" one.
But, in 210.52(C), it says "receptacles for countertops..." These "extra" receptacles are clearly not "for countertops," so they're allowed.Take another look at 210.52(C)(5) and its exception. They tell us where "receptacles" are to be mounted. But they do not limit that instruction to "the required minimum number of receptacles." So I infer that if you put a receptacle on an island or peninsula, it must be located where 210.52(C)(5) tells us to locate it, even if it is an "extra" one.
Chris even agrees with me.
Scary thought, isn't it Chris? :wink:
FWIW, I agree as well.
I see that I am not getting much support for my point of view. That?s a first! :wink:
Let me just make a few points, after which you are all welcome to continue to disagree with me.
? Putting a receptacle in the space well below an island or peninsular countertop, and claiming you don?t intend it to serve the countertop, is a stretch. You might as well put an ?extra? receptacle in a wall counter space, not protect it with GFCI, and claim it doesn?t have to be GFCI protected because it is not one of the ones required to serve the countertop. It?s there; it counts.
? 210.52(C)(5) tells us not to put receptacles more than 12 inches below the counter. It gives no leeway for ?extra? receptacles. It?s there; it counts.
? THE BIG REASON: The difference between this situation and putting a wall receptacle 6 feet above the floor is that it is not dangerous to have a receptacle that high. Nobody is going to trip over a wire plugged into that receptacle. It may be simply inconvenient (unless you have a TV there), but it is not dangerous. However, people are going to work at, or perhaps even sit next to, an island or peninsula countertop area. Putting a receptacle too far below the countertop surface, or putting it under an large overhang, is dangerous. Someone standing or sitting near the countertop is likely to bump into a cord that is plugged in there. That will cause the appliance to fall into their lap or onto their feet. It does not matter if the receptacle is just 13 inches below the countertop, or is at toe kick level. It is dangerous.
I am aware of the date. :smile: Sorry to disappoint, but this is my honest view of the situation.April 1'st isn't 'till tomorrow. This has to be a joke :smile:
I am aware of the date. :smile: Sorry to disappoint, but this is my honest view of the situation.