- Lockport, IL
- Semi-Retired Electrical Engineer
Re: Kitchen island receptacles
Yes. That is what I am saying. Or more to the point, that is what I believe the words in the NEC are saying.Originally posted by jim dungar: Charlie, are you saying that no receptacle can be mounted anywhere on an island unless it meets 210.52(C) requirements?
There is no distinction between receptacles that serve countertop appliances and receptacles that don't (i.e., that are meant for other purposes). If the receptacle is on the island, then it serves the "counter space." The rules that apply start at 210.52(C), as I mentioned in my first post. Once you start down the path set by that rule, there is no option given to you to install a receptacle that does not fit the rules.Originally posted by jim dungar: 210.52(C)(5) says the location for counter receptacles will be above the counter top. To be mounted below the counter top and still count as a counter receptacle you must meet requirements 1 or 2 of the exception. If the receptacle location does not meet the exception then it is not prohibited but rather it can not be considered a countertop receptacle.
That is a different game entirely. It was recently debated on this Forum. Please note this earlier post, which I believe was intended as a allusion to the earlier debate:Originally posted by jim dungar: I believe that if the island is acting as a room divider then it is subject to 210.52(A)(2)(3) and must have a general use receptacle mounted in/on it.
I am not either. But can we set this question aside, until we get through the other?Originally posted by electricmanscott: There are some who would argue that the back side of an island is wall space and you would have no choice but to install receptacles there anyway (I am not one of those people).