jimwalker
- TAMPA FLORIDA
Re: Kitchen Peninsula Receptacle
Now look what you did Allen inspectors.
I agree that the end of a counter does not count, if the counter ends in open space. But what if it ends at a wall? Am I reading this wrong?Originally posted by jwelectric: You don?t count the end of a counter top. The counter starts in the corner not from the front edge.
I set an 8 in. drawer then a sink and another 24 in. drawer for this peninsular. Would I be required to install a receptacle on the 8 in. side due to the 24 in. depth of the counter that I started the peninsular from? 8 plus 24= 32Originally posted by jimwalker:
"Should this 12 in. counter be against a wall would it now become a 36 in. counter and require two receptacles?"
just put it in the middle
If it was against a wall would it be a 30 inch counter?Originally posted by jimwalker:
Why do they draw the line at 12 inches ? I could put a toaster on a 6 inch counter
I believe the intent of "along the wall line" is the wall line that in in line with the connecting edge (front edge of counter) this would seem to ignore a side wall if the connecting edge ends at the side wall? As Mike said the intent is so there is an available receptacle within 24" of any counter space that requires a receptacle with the exception of Island and Peninsular Counter Spaces. How would you apply this if you had a counter that was over 24" deep? this is why I think "along the wall line" allows us to ignore the depth of a counter and just go by the wall line that has a connecting edge parallel to it. If the connecting edge stops at a wall so does the "wall line"(1) Wall Counter Spaces. A receptacle outlet shall be installed at each wall counter space that is 300 mm (12 in.) or wider. Receptacle outlets shall be installed so that no point along the wall line is more than 600 mm (24 in.) measured horizontally from a receptacle outlet in that space.