Sometimes you have to be careful.Originally posted by romeo:
Goldstar thanks for the reminder to identify the neutral. It could be a disaster to reverse the hot and neutral.
romeo
Use a 4" square plastic box--carlon B432, blank cover A400. If you don't have loom, use a piece of romex sheath. Slide into box, under clamp.Originally posted by peter d:
It's been a while, but this is how I do it. I use plain old NM connectors, cut a piece of the K&T loom, slide it over the K&T conductor, and then put the whole assembly into the rx connector, which is conveniently attached to a 4" square box.![]()
Suggestion: A wiggie and an extension cord (in a known-properly-wired receptacle) make great a diagnostic-tool combination.Originally posted by romeo:
Goldstar thanks for the reminder to identify the neutral. It could be a disaster to reverse the hot and neutral.
romeo
300.16(A) is the exception to the rule: "All splices go in boxes."A fitting used for this purpose shall contain no taps or splices and shall not be used at luminaire (fixture) outlets.
In many single family dwellings the walls, floors and ceilings are non-conductive. 250.110(1) has application, upon occasion, and describes how the box actually can be left ungrounded.Originally posted by wireman3736:
Something is missing here, there's something in the NEC about grounding the metal box, some people are so forgetful.
On the contrary, as I read 410.18, I read it as having two minds. One is as you describe, and the other is as I describe.Originally posted by wireman3736:
Article 410.18 settles this argument.
410.18 says it can be grounded or ungrounded.410.18 Exposed Luminaire (Fixture) Parts
(A) Exposed Conductive Parts Exposed metal parts shall be grounded or insulated from ground and other conducting surfaces or be inaccessible to unqualified personnel. Lamp tie wires, mounting screws, clips, and decorative bands on glass spaced at least 38 mm (1 1/ 2 in.) from lamp terminals shall not be required to be grounded.
250.110 Equipment Fastened in Place or Connected by Permanent Wiring Methods (Fixed)
Exposed non?current-carrying metal parts of fixed equipment likely to become energized shall be grounded under any of the following conditions:
</font><font size="2" face="Verdana, Helvetica, sans-serif">
- <font size="2" face="Verdana, Helvetica, sans-serif">Where within 2.5 m (8 ft) vertically or 1.5 m (5 ft) horizontally of ground or grounded metal objects and subject to contact by persons</font>