Knob and Tube Connectors

Status
Not open for further replies.
Re: Knob and Tube Connectors

Goldstar thanks for the reminder to identify the neutral. It could be a disaster to reverse the hot and neutral.

romeo
 
Re: Knob and Tube Connectors

Originally posted by romeo:
Goldstar thanks for the reminder to identify the neutral. It could be a disaster to reverse the hot and neutral.

romeo
Sometimes you have to be careful.
If something shorted the Hot (to say, metal lath, for example), you might find that someone has switched the Hot and Neutral in the panel. :eek:
 
Re: Knob and Tube Connectors

Al
Great excerpt from the white book. I did not know that.
I retract my "holy grail" statement about new equipment not being listed for k&t
 
Re: Knob and Tube Connectors

Originally posted by peter d:
It's been a while, but this is how I do it. I use plain old NM connectors, cut a piece of the K&T loom, slide it over the K&T conductor, and then put the whole assembly into the rx connector, which is conveniently attached to a 4" square box. :cool:
Use a 4" square plastic box--carlon B432, blank cover A400. If you don't have loom, use a piece of romex sheath. Slide into box, under clamp.
Excellent interface for romex wire.
Peter D's way works great if you need to go to BX, MC, AC, EMT, IMC, GRC, PVC, etc.
 
Re: Knob and Tube Connectors

Originally posted by romeo:
Goldstar thanks for the reminder to identify the neutral. It could be a disaster to reverse the hot and neutral.

romeo
Suggestion: A wiggie and an extension cord (in a known-properly-wired receptacle) make great a diagnostic-tool combination.

You literally have a reference hot, neutral, and ground in your hand.
 
Re: Knob and Tube Connectors

The reason I ask is the metal box conundrum. Like Bob points out, 300.20.

I'd really like to see a demonstration of this inductive heating from two 15 or 20 amp conductors passing through a 1/16" box wall. But I don't write this stuff.

There are a lot of cases where plastic just isn't my favorite choise. Peter and Romeo mentioned my favorite, that doesn't comply, but that's still what I think is best.

Al brought up 300.20(B). I hadn't thought about it applying to a box but it looks like it does.

Edit: I think keyboard caused character drops where Error D

[ January 20, 2006, 05:06 PM: Message edited by: physis ]
 
Re: Knob and Tube Connectors

You also have the 300.16(A) issue which requires a seperately bushed hole for each conductor. Unless you have a special fitting which looks like a straight weatherhead (service entrance cap that goes on top of a raceway).

What the heck are you doing anyway??
 
Re: Knob and Tube Connectors

Hi Larry,

This doesn't come from anything impractical that I'm doing right now. I work with K&T a lot and I just kinda don't get why it seems like there's an accepted allowance for code violations with this.

I wasn't aware of a legal method for going to a metal box with K&T until Al pointed out that you can use 300.20(B) and take a hack saw to the box.

Romeo has a legal solution with going to a plastic box first. Not usually all that practical though.

And I might as well gripe about some code language a little.

300.16. A box or terminal fitting having separately bushed holes for each conductor.......

Does that mean you can use a box period or that a box must also have separately bushed holes for each conductor?

What's a terminal fitting? I hope I'm not missing something obvious here but I'm trying to imagine all kinds of goofy things that a terminal fitting might be and I don't get it unless maybe I assume it's a connector. Either that or a wire lug, I don't think it's that.

Are there any connectors available with two separately bushed holes? I've never seen any.

Why does 300.20 address "phase" conductors instead of ungrounded conductors? That's pretty wierd language. Does phase conductors include ungrounded single phase conductor? I'd think it would but then why not call the things ungrounded conductors?

But it's not the code language I'm concerned with so much. It's that code violations seem to be commonly accepted. I'd say safe for the most part as well.

So should the code have some broader allowances for terminating K&T to metal boxes?
 
Re: Knob and Tube Connectors

300.16(A) is an interesting animal. The last sentence in it offers an important clue:
A fitting used for this purpose shall contain no taps or splices and shall not be used at luminaire (fixture) outlets.
300.16(A) is the exception to the rule: "All splices go in boxes."

The "fitting" is where the cable sheath or raceway ends and the internal conductors continue.

The fitting is directly analogous to a service weatherhead, only smaller and needing only to be suitable for dry locations away from direct sunlight. Two of the old slang names for the fitting were monkey face or birds foot.

The conductor emerging from the raceway or cable splices to the open wiring or concealed K&T with a "flying splice" using "approved slicing devices" - see 394.56. - that is wire nuts, among other things.
 
Re: Knob and Tube Connectors

Courtesy of Electricmanscot and ECN: Note there are three "fittings" in the photo.

KnobTube4.jpg
 
Re: Knob and Tube Connectors

YES
Al,
That's what I was thinking of. Good luck finding any I would think. DO they still make them.

As far as the metal boxes and the slots. Someone posted, here I think (maybe ECN), that the older versions of the Code allowed seperate holes in ferrous metal enclosures when under 50 amps. I don't have any dates or more details on that. In seems 300.16 may be a hold over and just forgotten. Who knows?
 
Re: Knob and Tube Connectors

In a pinch, I contend, that if I take a 1/2" weatherhead that is threaded for 1/2" NPT, I can screw into that female the connector or my choice.

Say, for romex, I could screw in a plain old 3/8" two screw romex clamp (sans locknut).

The clamp secures the end of the sheath and the conductors emerge from the "fitting" through the black bakelite of the weatherhead.
 
Re: Knob and Tube Connectors

That's a really wierd setup in that photo. :D

[ January 24, 2006, 01:52 PM: Message edited by: physis ]
 
Re: Knob and Tube Connectors

Originally posted by wireman3736:
Something is missing here, there's something in the NEC about grounding the metal box, some people are so forgetful.
In many single family dwellings the walls, floors and ceilings are non-conductive. 250.110(1) has application, upon occasion, and describes how the box actually can be left ungrounded.
 
Re: Knob and Tube Connectors

If I were putting K&T in a metal box I most likely would be connecting circuit conductors with EMT, NM or MC as well. Presto, there's an EGC present.
 
Re: Knob and Tube Connectors

Leaving a metal j-box ungrounded when connected to K&T occurs most commonly, in my experience, when I have to cut in a box to support a new luminaire. When the luminaire location is already supplied by existing K&T, and the old fixture was screwed to the plaster and lathe, I am bound to install a box when I replace the luminaire with a modern luminaire.

In most spaces, the luminaire location is more than 5 feet horizontally and 8 feet vertically from a grounded surface, and 250.110(1) applies nicely.
 
Re: Knob and Tube Connectors

Sorry Al but I'll have to disagree with you on 250.110 (1). This is not an exception to grounding, It's telling you if it falls within these dimensions that it shall be grounded, just because it's above 8' doesn't allow it to override other sections of the code. Article 250.112 (J) sends you to part 5 in article 410, Article 410.18 settles this argument.I know it's common practice to replace metallic fixtures on ungrounded circuits with new metallic fixtures but it doesn't meet code without GFCI protection.
 
Re: Knob and Tube Connectors

Originally posted by wireman3736:
Article 410.18 settles this argument.
On the contrary, as I read 410.18, I read it as having two minds. One is as you describe, and the other is as I describe.
410.18 Exposed Luminaire (Fixture) Parts
(A) Exposed Conductive Parts
Exposed metal parts shall be grounded or insulated from ground and other conducting surfaces or be inaccessible to unqualified personnel. Lamp tie wires, mounting screws, clips, and decorative bands on glass spaced at least 38 mm (1 1/ 2 in.) from lamp terminals shall not be required to be grounded.
410.18 says it can be grounded or ungrounded.

Air, distance and non-conductive building materials make a good insulation from ground, especially in a wood framed dwelling with plaster on wood lathe and a wood floor. The most common grounded surfaces that might be in that room will be the cast iron radiator and its pipes, or metal grating in contact with metal ductwork.

250.110(1) spells out the distances within which grounding is required. Outside of those distances, grounding may, or may not, be done. . .it's just not required to be done.
250.110 Equipment Fastened in Place or Connected by Permanent Wiring Methods (Fixed)

Exposed non?current-carrying metal parts of fixed equipment likely to become energized shall be grounded under any of the following conditions:
</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Where within 2.5 m (8 ft) vertically or 1.5 m (5 ft) horizontally of ground or grounded metal objects and subject to contact by persons</font>
<font size="2" face="Verdana, Helvetica, sans-serif">
 
Re: Knob and Tube Connectors

since when is it legal to make an extension
from
an ungrounded system or to add a new device or fixture that is required tobe grounded. I see this all the time here in colorado.the Home owner or the DIY adds new duplex recpticel
or a new light fixture climbs in the attic cuts the K&T and splice a pice of 2 wire nm cable to he K&T then adds
the duplex or light fixture.
you are making a tap from an ungrounded system
I see this alot on the old 2 wire black rigid pipe jobs too.
 