KWH TO KW- generator sizing

We do when our backup generators are inverter based.
An inverter output generator possibly shuts it's output off to protect itself much sooner than any overcurrent device will trip when the starting current exceeds a certain level. On conventional alternator output the impedance of the alternator is current limiting and essentially it acts like a soft starter when attempting to start a larger motor load. It will drag voltage of everything else that is running down as well during that starting operation.
 
An inverter output generator possibly shuts it's output off to protect itself much sooner than any overcurrent device will trip when the starting current exceeds a certain level. On conventional alternator output the impedance of the alternator is current limiting and essentially it acts like a soft starter when attempting to start a larger motor load. It will drag voltage of everything else that is running down as well during that starting operation.
Obviously I know that or I wouldn't have made my comment.
 
(Ok, it's still weird when you quote and respond to my post like that without adding a phrase or two to explain that your doing so "Just to elaborate" or "For whoever is curious what this means...")
My bad, I realize I tend to do that often. will try to do better and add things like "just to elaborate" in the future.
 
So if my utility company can’t provide peak KW then I need to size off either a load calc or a more general size based on loads ect. Thanks so much for this response and help.
One possibility that some utilities will do is measure kWh over a 5 minute or 15 minute period, which you can then multiply by 12 or 4 (depending on if it is 5 or 15 minute kWh), and since the kWh is a relative short period, you can get closer to what the maximum demand is for the service when you choose the highest reading for the month / year, then apply that to your generator size.
 
Here is an example of what everyone has been saying about how you cannot use kWh to determine kW requirements;

kWh is kW divided by time, in hours. So 100kWh is 100kW continuously for 1 hour, in which case the PEAK REQUIREMENT from the source of that power is 100kW.

But if you used 1,000kW for only 6 minutes (0.1 hours) and nothing else, that is STILL only 100kWh on the meter, but the PEAK REQUIREMENT was 1,000kW. So if you had sized a generator based on that 100kW value and your load needed 1,000kW for only 10 minutes, your generator will fail.

So again, you need the “peak demand” values from the utility.
 