We do when our backup generators are inverter based.
That sounds like a portable. I don't play with them. Too much customer interaction, not usually good.
We do when our backup generators are inverter based.
An inverter output generator possibly shuts it's output off to protect itself much sooner than any overcurrent device will trip when the starting current exceeds a certain level. On conventional alternator output the impedance of the alternator is current limiting and essentially it acts like a soft starter when attempting to start a larger motor load. It will drag voltage of everything else that is running down as well during that starting operation.We do when our backup generators are inverter based.
Obviously I know that or I wouldn't have made my comment.An inverter output generator possibly shuts it's output off to protect itself much sooner than any overcurrent device will trip when the starting current exceeds a certain level. On conventional alternator output the impedance of the alternator is current limiting and essentially it acts like a soft starter when attempting to start a larger motor load. It will drag voltage of everything else that is running down as well during that starting operation.
other people read this.Obviously I know that or I wouldn't have made my comment.
(Ok, it's still weird when you quote and respond to my post like that without adding a phrase or two to explain that your doing so "Just to elaborate" or "For whoever is curious what this means...")other people read this.
My bad, I realize I tend to do that often. will try to do better and add things like "just to elaborate" in the future.(Ok, it's still weird when you quote and respond to my post like that without adding a phrase or two to explain that your doing so "Just to elaborate" or "For whoever is curious what this means...")
One possibility that some utilities will do is measure kWh over a 5 minute or 15 minute period, which you can then multiply by 12 or 4 (depending on if it is 5 or 15 minute kWh), and since the kWh is a relative short period, you can get closer to what the maximum demand is for the service when you choose the highest reading for the month / year, then apply that to your generator size.So if my utility company can’t provide peak KW then I need to size off either a load calc or a more general size based on loads ect. Thanks so much for this response and help.