Labeling Full Load Current for panels with VFDs.

Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Following on this thread. Do we still need to consider the inrush current of a motor? Given that your using VFD controller
When do you consider the inrush current of the motor? The requirements for the VFD do not change the requirements for the motor. The VFD may change the current via programming of parameters but it does not change conductor size. I may change parameters tomorrow.
 

iLeKtRiKoS

Member
Location
AB, Canada
Occupation
Electrical designer & estimator
When do you consider the inrush current of the motor? The requirements for the VFD do not change the requirements for the motor. The VFD may change the current via programming of parameters but it does not change conductor size. I may change parameters tomorrow.
Oh sorry for design purpose
 