quogueelectric
Senior Member
- Location
- new york
You reminded me to mention rigid 90s if 90s are put in otherwise sometimes the string cuts right thru the pvc and creates nightmares.growler said:Why do all of that. You can make an 800 ft pull easy enough if it's only 3 ea #8s and 1 ea #10 in 1" pvc. Where people mess up is putting factory 90's on the ends before pulling the cable. If you just leave the conduit sticking straight out of the trench on each end, pull the cable first and then install the 90's it's much easier. Friction is what kills a wire pull and every bend developes friction ( so don't have any if you can keep from it ).
It's easier to pull through 800 ft of straight conduit than it is to pull through 400 ft with say 180 degrees of bend in it. If the people feeding know to keep the conductors straight and there are no dirty couplings and gravel. Lots of good wire lube to reduce friction and it's a piece of cake.