I think the op needs a picture of this. I just put one in that had a lug for this but i didn't take one. Most of the ones I install don't have a lug for this thoughYes, add the code required main bonding jumper in the service equipment and remove the EGC. Note that is not even the correct term for that conductor as it is on the line side of the OCDP, and is actually a Supply Side Bonding Jumper and not an EGC.
There is no issue with connecting the GEC to the neutral in the meter can. Most meter cans have a lug for that purpose. The connection of the GEC in the meter is compliant with the code.