I'm just revisiting the requirements for the Laundry Room in what I will refer to as a Single Family Dwelling for simplicity.
In the past, the way I've always done it, and seen it done, is (1) Dedicated 20A Circuit for (1) (15/20A) (Simplex/Duplex) Receptacle for the Washer/Dryer.
No other outlets on that circuit, none.. not even in the laundry area/room. That's just the way I've seen it done and have done it.
However, the question seems to be one that is raised a lot, based on my searches, as to whether or not other receptacles, sometimes referred to as "convenience receptacles" or what would essentially amount to "general purpose receptacles" within the laundry area are allowed on that 20A Laundry Branch Circuit. I say NO.
I just want to get your take on my interpretation of the code.
When reading 210.52(F) where it says "...at least one..." it implies that there could be more than one receptacle, BUT taken in combination with 210.11(C)(2) as meaning that my initial interpretation above is the correct one.
210.11(C)(2) - Requiring a 20A Branch Circuit with no other outlets for that which is required by 210.52(F).
210.52(F) - Requires a minimum of ONE receptacle outlet.
Essentially I'm saying that if you read 210.52(F) by itself, the phrasing "at least one" implies there could be more than one, but if you read the two sections TOGETHER, it's saying that there has to be a dedicated 20A circuit supplying one receptacle outlet with no other outlets. That if you put other outlets in the room they have to be on a separate circuit.
Thoughts?
In the past, the way I've always done it, and seen it done, is (1) Dedicated 20A Circuit for (1) (15/20A) (Simplex/Duplex) Receptacle for the Washer/Dryer.
No other outlets on that circuit, none.. not even in the laundry area/room. That's just the way I've seen it done and have done it.
However, the question seems to be one that is raised a lot, based on my searches, as to whether or not other receptacles, sometimes referred to as "convenience receptacles" or what would essentially amount to "general purpose receptacles" within the laundry area are allowed on that 20A Laundry Branch Circuit. I say NO.
I just want to get your take on my interpretation of the code.
When reading 210.52(F) where it says "...at least one..." it implies that there could be more than one receptacle, BUT taken in combination with 210.11(C)(2) as meaning that my initial interpretation above is the correct one.
210.11(C)(2) - Requiring a 20A Branch Circuit with no other outlets for that which is required by 210.52(F).
210.52(F) - Requires a minimum of ONE receptacle outlet.
Essentially I'm saying that if you read 210.52(F) by itself, the phrasing "at least one" implies there could be more than one, but if you read the two sections TOGETHER, it's saying that there has to be a dedicated 20A circuit supplying one receptacle outlet with no other outlets. That if you put other outlets in the room they have to be on a separate circuit.
Thoughts?