Laundry Receptacle Req

Status
Not open for further replies.

seabeece

Member
I am curious if there is a minimum height required for laundry room receptacle for the washing machine or if it just falls under the regular receptacle requirements
 
Re: Laundry Receptacle Req

Being as how (as far as I know) it can be mounted in the floor, and I don't know of anything that says it can't be below the floor, there is no minimum hieght.

I can't think of anything that restricts it.
 
Re: Laundry Receptacle Req

210.50 (C) Appliance Outlets. Appliance receptacle outlets installed in a dwelling unit for specific appliances, such as laundry equipment, shall be installed within 1.8 m (6 ft) of the intended location of the appliance.

210.52 Dwelling Unit Receptacle Outlets.
This section provides requirements for 125-volt, 15- and 20-ampere receptacle outlets. Receptacle outlets required by this section shall be in addition to any receptacle that is part of a luminaire (lighting fixture) or appliance, located within cabinets or cupboards, or located more than 1.7 m (5? ft) above the floor.
 
Re: Laundry Receptacle Req

210.50 (C) Appliance Outlets. Appliance receptacle outlets installed in a dwelling unit for specific appliances, such as laundry equipment, shall be installed within 1.8 m (6 ft) of the intended location of the appliance.

210.52 Dwelling Unit Receptacle Outlets.
This section provides requirements for 125-volt, 15- and 20-ampere receptacle outlets. Receptacle outlets required by this section shall be in addition to any receptacle that is part of a luminaire (lighting fixture) or appliance, located within cabinets or cupboards, or located more than 1.7 m (5? ft) above the floor.


I don't think that either of these sections would apply to the height of a laundry receptacle.
 
Re: Laundry Receptacle Req

The question was:

I am curious if there is a minimum height required for laundry room receptacle for the washing machine or if it just falls under the regular receptacle requirements
My reply was to answer with code the requirements for the laundry receptacle:
210.50 (C) with-in six feet
210.52 no higher than five and a half feet from the floor
both statements are the requirements for the installation for the laundry receptacle. The receptacle is required to be with-in six feet and no higher than five and a half feet high.

I challenge you to show me more.
:)
 
Re: Laundry Receptacle Req

I shall meet your challenge. The code says within 6 feet of the appliance and makes no reference to the hight from the floor.The distance is the reference distance to the applianc. Hence the outlet could be next to the floor and still be within 6 ft. 210.52 does not apply either.IMHO
210.52 says the cannot be more than 5 1/2 feet above the floor. I am extracting this from the illustrated guide to the electric code by miller based on the 2002 code. page 131.

[ April 25, 2005, 07:53 PM: Message edited by: stew ]
 
Re: Laundry Receptacle Req

Well we do agree on the fact that the receptacle can be no futher away than six feet from the appliance as outlined by 210.50 (C) Appliance Outlets. Appliance receptacle outlets installed in a dwelling unit for specific appliances, such as laundry equipment, shall be installed within 1.8 m (6 ft) of the intended location of the appliance.

I will agree that the five and a half rule might not count for the laundry because of the header, 210.52 Dwelling Unit Receptacle Outlets. I believe that this requirement is for the receptacles required for wall space.
;)

[ April 25, 2005, 09:29 PM: Message edited by: jwelectric ]
 
Re: Laundry Receptacle Req

We usually put outlet @ 36" AFF.

The main reason is that it does not fall in the seams of the sheetrock (48"). If the painter falls behind, floated or not, we are trimming it out. (device only) This is the only reason we put it at this elevation.

Sometimes you have to think outside of the Bun.
 
Re: Laundry Receptacle Req

I would say article 210.52 in the NEC 2002 does apply to the receptacle outlet in the laundry room, I cannot see any reason why it would not ??
 
Re: Laundry Receptacle Req

210 52 5 1/2 ft pertains to required receptacle for wall spacing.210.50 C has no constraints 6 ft.,so if the washer had a 6 ft cord mounted at 3 ft AFF & 6 ft the receptacle could within 9 ft aff :D
 
Re: Laundry Receptacle Req

O.K. Still believe 210.52 does apply to the laundry room receptacle height........
In summary of this article , one would think that if you place a receptacle over the 5 1/2 ft. mark you "WOULD NOT" be meeting the requirements of 210.52(F).

This is now I am looking at this and leave room to stand corrected if wrong.
 
Re: Laundry Receptacle Req

Originally posted by drg:
O.K. Still believe 210.52 does apply to the laundry room receptacle height........
In summary of this article , one would think that if you place a receptacle over the 5 1/2 ft. mark you "WOULD NOT" be meeting the requirements of 210.52(F).

This is now I am looking at this and leave room to stand corrected if wrong.
You're good, but missing a key part.

Your assumption is, since the first paragraph of 210.52 spec's the 5.5', and 210.52(F) exists, then (F) must comply with the general requirements of 210.52.

So a laundry receptacle must be below 5.5'.

That doesn't have to be the receptacle for the washer. :D

210.52 states that receptacles required by it are in addition to receptacles located above 5.5' off the deck. So, as long as one exists, (F) is satisfied, and you can put the washer outlet at 8'. :D
 
Re: Laundry Receptacle Req

Originally posted by allenwayne:
210 52 5 1/2 ft pertains to required receptacle for wall spacing.
I thought so too, but it doesn't.

The first paragraph of 210.52 is "lord" over all it's subcategories.

Wall Spacing comes after, in (A). So all receptacles specified in (A) - (H) have to fall in line. :eek:

Good eye, drg!
icon14.gif


[ April 26, 2005, 07:49 AM: Message edited by: georgestolz ]
 
Re: Laundry Receptacle Req

The part in the 210.52 article that makes me think this way is the (SHALL BE IN ADDITION).

Thanks for the response.
:)
 
Re: Laundry Receptacle Req

Yes, you did a fine job of answering him in your first post and we applaud you on a job well done
:p
 