frizbeedog
Senior Member
- Location
- Oregon
steelersman said:then what are you supposed to plug your 120 volt washer into if all that's there is a 30 amp 220 volt plug?
I assume he's talking about a stack, one which uses just a 30 recep.
steelersman said:then what are you supposed to plug your 120 volt washer into if all that's there is a 30 amp 220 volt plug?
right on. What I used to think of as a very simple task and went about doing without even using any brain power has now been turned into something that is now so GD confusing my brain feels like it's about explode! Man oh man some of you guys on here want to make everything so GD complicated. This isn't rocket science. Put a dryer outlet in and put a dedicated 20 amp 120 V washer outlet in and that's it.480sparky said:Means nothing to me. It's my AHJs that count.
From dictionary.com:
I don't see an iron mentioned there.
steelersman said:Put a dryer outlet in and put a dedicated 20 amp 120 V washer outlet in and that's it.
celtic said:"What if" the "laundry room" is no more than the width and depth of the combo washer/dryer ?
Imagine if you will, a closet sized area (with a bi-fold door) that allows ONLY for the W/D and nothing else....going a step further, this W/D location is in a hallway.
celtic said:So where do we place the 120v recept. when the W/D is a 240v 30A combo in the location detailed above?
You cheated!480sparky said:Right outside the 'area' where the stack unit is. In the hallway. Nothing says it has to be behind or directly beside the stack unit.
celtic said:Could I put it the 120v recept. on another floor?
LMAOfrizbeedog said:Troublemaker. :grin:
46 pages for sure.
celtic said:Chance to redeem yourself:
Could I put it the 120v recept. on another floor?
celtic said:Someone claimed it's not rocket science....
![]()
480sparky said:I say not. It is to be installed for the laundry. If the laundry is in this 'area', then that's where the circuit & receps gotta go.
Not unlike trying to put your two SABCs in the garage instead.
celtic said:I disagree
Hint:
The SABC req. is pretty specific.
480sparky said:On which one? The laundry placement or the SABC placement?
celtic said:So where do we place the 120v recept. when the W/D is a 240v 30A combo in the location detailed above?
celtic said:Think about it for a second...the SABC req. is pretty specific ~ can the same be said about the 120v for the laundry?
480sparky said:On which one? The laundry placement or the SABC placement?
place it right next to or above or below the dryer outletceltic said:So where do we place the 120v recept. when the W/D is a 240v 30A combo in the location detailed above?
frizbeedog said:210.52 (F) makes no metion as to where this recep is to be placed.
....."for the laundry."
stickboy1375 said:Again, not rocket science.
frizbeedog said:..... I am a rocket scientist.....![]()
480sparky said:Annnnnd, where is the laundry? Hopefully, near where 210.50(C) says it is.