18-30 Log #3561 NEC-P18 Final Action: Accept in Principle
(406.3(D)(4) (New) )
_______________________________________________________________
Submitter: James T. Dollard, Jr., IBEW Local 98
Recommendation: Add a new list item to 406.3(D) as follows:
406.3(D)(4) Arc-Fault Circuit Interrupters. Arc-Fault circuit-interrupter protected receptacles shall be provided where replacements are made at receptacle outlets that are required to be so protected elsewhere in this Code.
Substantiation: The NEC presently addresses receptacle replacement in 406.3(D). This proposal seeks to expand the present receptacle replacement requirements to include arc fault protected receptacles where required elsewhere in the NEC. The existing requirement in 406.3(D)(2) requires GFCI protected receptacles where replacements are made at receptacle outlets that are
required to be so protected elsewhere in the NEC. There is no practical reason to limit the level of safety provided by AFCI’s to new homes only.
The benefits of 210.12 have been well substantiated over the last few NEC cycles, but it is highly unlikely that the fire-reducing provisions of 210.12 will ever result in AFCI protection for existing dwelling units unless branch-circuit circuit breakers are replaced or the service is upgraded. There is no practical reason to limit the level of safety provided by an AFCI to new homes only.
This proposal will provide that extra protection for older homes by requiring the gradual replacement, over time, of non-AFCI-protected receptacles with new AFCI-protected ones.
Panel Meeting Action: Accept in Principle
Add a new (4) to 406.3(D) as follows:
406.3(D) (4) Arc-Fault Circuit-Interrupters. Listed combination arc-fault circuit interrupter receptacles shall be provided where replacements are made at receptacle outlets that are required to be so protected elsewhere in this code.
Exception: Unless the receptacle is protected by an upstream AFCI.
Panel Statement: CMP-18 edited the proposed text for clarity.
Number Eligible to Vote: 11
Ballot Results: Affirmative: 9 Negative: 2
Explanation of Negative:
LOWRANCE, JR., A.: The panel in accepting this proposal has not taken into account the magnitude of this new requirement. In requiring the replacement receptacle, in areas required to be Arc Fault Circuit Interrupter protected, to be an AFCI receptacle type the panel is, in a large amount of the cases, requiring the circuit to be completely rewired. Many older houses have circuits with
shared neutrals, multi wire branch circuits, loose connections, and degraded insulation. In all of these cases the wiring would have to be replaced for the AFCI receptacle to function.
Additionally the homeowner would be tempted to do the replacement his or her self thus bypassing the electrical installation
professional who is acquainted with the hazards inherent in such installations. Enforceability is an additional issue in this change as again the homeowner would be tempted to do the work his or her self without taking advantage of the benefits that an inspection can provide.
We need more experience to be obtained regarding the installation of combination type AFCIs in new dwellings before requiring the installation of AFCIs in wide variety of existing dwellings that will have numerous different wiring configurations.”
TODD, S.: The replacement of the receptacle on a circuit with the Combo AFCI receptacle will only protect the circuit down stream from the AFCI from parallel and series arcs and upstream from series arcs. The Submitter’s substantiation is to make a requirement similar to the receptacle replacement where GFCI receptacles are required elsewhere in the code. The justificationdid not include any documented problems in the field of a safety concern.
Many receptacles are replaced by homeowners who may or may not replace the receptacle with and AFCI type receptacle. This proposed requirement is unenforceable. The committee discussed the operational issues of combining
the AFCI technology with old construction. In addition, if the circuit is protected by an AFCI type circuit breaker then a standard receptacle is acceptable.
Comment on Affirmative:
COSTELLO, P.: The new requirement will now provide AFCI protection to those receptacles in older homes where it would be required today. This is a proactive approach to providing extra protection to a homes aging wiring system.
WELLS, J.: I am voting affirmatively because I believe the submitter has appropriately endeavored to address the problem of electrical fires in existing dwellings. Data indicates that a very significant portion of electrical fires, in fact, occur is such older homes.
During the comment period, I encourage the submitter and others to address what I consider flaws in the wording as Accepted in the panel action. First, the wording should allow AFCIs of either the circuit breaker or outlet branch circuit type to be used in a non discriminatory way for compliance. Second, I am not certain that replacement of an individual receptacle should serve as the
trigger for requiring AFCI protection in existing buildings. Alternative triggers should be considered and proposed during the comment period.