2-97 Log #3259
(210.11(C)(2)(a))
Panel statement;
"The intent of this section is to require at least one 20-
ampere branch-circuit that is dedicated to the laundry area to ensure that the
branch circuit is sufficiently sized to supply electrical equipment associated
with doing laundry, such as an iron.
Receptacles installed in a laundry area
intended to serve laundry equipment must comply with 210.11(C)(2) as
presently written. The requirements in section 210.11 do not preclude the
addition of other branch circuits in the laundry area."
Learning,.. always learning . it is not the area that matters most but rather , it is what the receptacle is intended to serve. Sometimes this is obvious and sometimes not .