Dave Richards
New member
Is a hollow post(pipe) for an outside gate considered an approved raceway?
The post has a cap on it making it "weather-proof".
Article 100-Raceway.
An enclosed channel of metal or nonmetallic
materials designed expressly for holding wires, cables, or
busbars, with additional functions as permitted in this
Code. Raceways include, but are not limited to, rigid metal
conduit, rigid nonmetallic conduit, intermediate metal conduit,
liquidtight flexible conduit, flexible metallic tubing,
flexible metal conduit, electrical nonmetallic tubing,
electrical metallic tubing, underfloor raceways, cellular
concrete floor raceways, cellular metal floor raceways,
surface raceways, wireways, and busways.
110.8 Wiring Methods.
Only wiring methods recognized
as suitable are included in this Code. The recognized methods
of wiring shall be permitted to be installed in any type
of building or occupancy, except as otherwise provided in
this Code.
300.1 Scope.
(A) All Wiring Installations. This article covers wiring
methods for all wiring installations unless modified by
other articles.
110.3(B)(B) Installation and Use.
Listed or labeled equipment
shall be installed and used in accordance with any instructions
included in the listing or labeling.
300.3(A) Single Conductors. Single conductors specified in Table 310.13(A) shall only be installed where part of a recognized wiring method of Chapter 3.
Pierre, I have a problem with your use of the term raceway. I do, however, agree with the availability of their use for running a cable wiring method. :smile:. . . as raceways as well.
Charlie and IBEW441bc have both provided good information on the types of listed raceways/wiring methods. I also see some who like to use mullions from window frames or gazebos as raceways as well.
Considering the posts above, can you change the gate post to RMC or IMC?
Roger
300.11(B) Raceways Used as Means of Support.
Raceways shall be used only as a means of support for other raceways,
cables, or nonelectrical equipment under any of the
following conditions:
(1) Where the raceway or means of support is identified for
the purpose
(2) Where the raceway contains power supply conductors
for electrically controlled equipment and is used to support
Class 2 circuit conductors or cables that are solely
for the purpose of connection to the equipment control
circuits
(3) Where the raceway is used to support boxes or conduit
bodies in accordance with 314.23 or to support luminaires
in accordance with 410.36(E)
Did you really think I was serious? See the wink. :wink:
Maybe my delivery was better than I thought.
Roger
but somebody might have....
Is that something like a "what if"
Roger
Again if the wiring method is cable I can certainly run it in a mullion. :smile:
. . . Open conductors in a mullion used as a raceway, no way. . .
Jesse, in light of his previous post, I don't believe that is what he meant. :smile:do you mean that you have seen something of the nature of THHN run in window mullions? . .
No, but you can use a wiring method that deos not require a raceway :smile: