The electrical drawings indicate that an automatic transfer switch and it's associated distribution panel is in the same room as the Incoming normal power distribution switchboard. Any opinions on whether this condition is contrary to the 2005 NEC?
Check out the thread's title.Is it legally required or optional?
No difference. It would be different if we were talking about emergency equipment. But it would not be the NEC that threw the flag on this play. It would be NFPA 110, paragraph 7.2.2.Big difference. Just asking.
Check out the thread's title.
No difference. It would be different if we were talking about emergency equipment. But it would not be the NEC that threw the flag on this play. It would be NFPA 110, paragraph 7.2.2.
Sorry, I may have caused confusion with my use of the word flag. All I meant was that (1) LRS and normal can share a room, that (2) emergency and normal cannot share a room, and that (3) it is the other NFPA document, and not the NEC, that says that emergency and normal cannot share a room.