(4) Countertop and Similar Work Surface Receptacle Outlets.
Receptacles installed for countertop and similar work surfaces as specified in 210.52(C) shall not be considered as the receptacle outlets required by 210.52(A).
(B) SmallAppliances.
(1) Receptacle Outlets Served. In the kitchen, pantry, break- fast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.ll(C)(l) shall serve all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets covered by 210.52(C), and receptacle outlets for refrigeration equipment.
Exception No. 1: In addition to the required receptacles specified by 210.52, switched receptades supplied from a general-purpose 15- or 2,()., ampm branch circuit as required in 210. 70(A)(l), Exception No. 1, shall be permitted.
Exception No. 2: In addition to the required receptacles specified l,y 210.52, a receptacle outlet to serve a specific appliance shall be permit- ted to be suppliedfrom an individual branch circuit rated 15 amperes or greatet:
(2) No Other Outlets. The two or more small-appliance branch circuits specified in 210.52(B) (1) shall have no other outlets.
Exception No. 1: A receptacle installed solely for the electrical supply to and support of an electric dock in any of the rooms specified in 210.52(B)(l).
Exception No. 2: Receptacles installed to provide power for supplemen- tal equipment and lighting on gas-fired ranges, ovens, or counter- mounted cooking units.