IIRC, for batteries with voltage higher than 50V the rules in the NEC change.
Yep, but there are a few interesting angles.
The bolded parts-
690.7? Weather correction factor? That would only apply DC to DC then? As in 690.72?
I hadn't heard of the "requiring steel cases" thing as of yet...isn't that more like "they require grounding", for some reason?
The most interesting is H- if the BESS is less than 5 feet away from what it's running, you're avoiding all that BOS after H...
And the buck boost thing- all it's saying is "use the right size wires for the amperage/voltage".
---
(B) Dwellings.
(1) Operating Voltage. Storage batteries for dwellings
shall have the cells connected so as to operate at a voltage
of 50 volts, nominal, or less.
Exception: Where live parts are not accessible during rou-
tine battery maintenance,
a battery system voltage in ac-
cordance with 690.7 shall be permitted.
D) Battery Nonconductive Cases and Conductive Racks.
Flooded, vented, lead-acid batteries with more than twenty-
four 2-volt cells connected in series (48 volts, nominal)
shall not use conductive cases or shall not be installed in
conductive cases. Conductive racks used to support the
nonconductive cases shall be permitted where no rack ma-
terial is located within 150 mm (6 in.) of the tops of the
nonconductive cases.
This requirement shall not apply to any type of valve-
regulated lead-acid (VRLA) battery or any other types of
sealed batteries that may require steel cases for proper op-
eration.
(H) Disconnects and Overcurrent Protection.
Where en-
ergy storage device input and output terminals are more
than 1.5 m (5 ft) from connected equipment, or where the
circuits from these terminals pass through a wall or parti-
tion, the installation shall comply With the following:
( I ) A disconnecting means and overcurrent protection shall
be provided at the energy storage device end of the
circuit. Fused disconnecting means or circuit breakers
shall be permitted to be used.
(2) Where fused disconnecting means are used, the line
terminals of the disconnecting means shall be con-
nected toward the energy storage device terminals.
(3) Overcurrent devices or disconnecting means shall not
be installed in energy storage device enclosures where
explosive atmospheres can exist.
(4) A second disconnecting means located at the connected
equipment shall be installed where the disconnecting
means required by 690.71 (H)(1) is not within sight of
the connected equipment.
(5) Where the energy storage device disconnecting means
is not within sight of the PV system ac and dc discon-
necting means, placards or directories shall be installed
at the locations of all disconnecting means indicating
the location of all disconnecting means.
---
690.72 Charge Control.
(A) General. Equipment shall be provided to control the
charging process of the battery. Charge control shall not be
required where the design of the photovoltaic source circuit
is matched to the voltage rating and charge current require-
ments of the interconnected battery cells and the maximum
charging current multiplied by 1 hour is less than 3 percent
of the rated battery capacity expressed in ampere-hours or
as recommended by the battery manufacturer.
AH adjusting means for control of the charging process
shall be accessible only to qualified persons.
Informational Note: Certain battery types such as valve-
regulated lead acid or nickel cadmium can experience ther-
mal failure when overcharged.
---
690.72(C) Buck/Boost Direct-Current Converters. When buck/
boost charge controllers and other dc power converters that
increase or decrease the output current or output voltage with
respect to the input current or input voltage are installed, the
requirements shall comply with 690.72(C)(1) and (C)(2).
(1) The ampacity of the conductors in output circuits shall
be based on the maximum rated continuous output cur-
rent of the charge controller or converter for the se-
lected output voltage range.
(2) The voltage rating of the output circuits shall be based
on the maximum voltage output of the charge control-
ler or converter for the selected output voltage range.