As I am trying to get my mind around (small as it may be) the entire business of generator grounded (neutral) and GES issues, I am making a list of points:
1. if the generator is wired (plugs) into a premises (dwelling) grounded (neutral), then only in ONE place can the grounded (neutral) and grounding system be connected. Usually at the first disconnect (circuit breaker panel) ONLY ONE - check
2. if the generator transfer switch switches the grounded (neutral) and the generator powers selected premises (dwelling) circuits, then it is a Separately Derived System (SDS) and attention should be paid to insure that the grounded (neutral) and grounding system is connected in one place, on-board the generator. ONLY ONE - check
Here's the rub -
3. the generator is in close proximity to a building, premises (dwelling); why not use the existing GES (grounding electrode system) to ground the generator and generator chassis??? If an argument is made that the existing GES is connected to the existing premises (dwelling ) wiring, and a separate electrode should be installed to insure a completely isolated set-up, I still can't see it (equipotential-wise), but I can understand the possibility of creating a loop.
4. in the case where the generator doesn't involve the premises (dwelling) wiring, and the generator is just used to power one or two pieces of equipment, e.g. - refrigerator, beer-meister, and is using an extension-cord set-up, I can buy the argument of no rod, unless the manufacturer requires. (no connection to existing electrode) But does it not create a problem with equipotential still, and does it hurt to bond-on to the existing GES???
5. I am intentionally staying away from non-building situations, for now; i.e. RV, motorhome, carnival.