winnie
- Springfield, MA, USA
- Electric motor research
Recently a discussion of the 'Leyton' transformer connection came up:
http://forums.mikeholt.com/showthread.php?t=182511
The 'Leyton' connection is purported to convert a single phase load into a balanced three phase load.
Hugh Leyton had previously joined the MH forum, but has not been active since joining to discuss the transformer connection:
http://forums.mikeholt.com/showthread.php?t=146298
I took part in an extensive discussion on the topic:
http://forums.mikeholt.com/showthread.php?t=176806
The Leyton connection is similar in concept to the 'zig-zag' connection of a three phase generator to produce single phase output, and is also related to the 'double-delta' connection of a 12 lead generator.
I contend that the Leyton connection will put similar current loading on all three phases of the connected transformers, but that the phase angle of this loading is still _single phase_. As such, I contend that the loading placed on the three phase supply is still _single phase_ loading.
As a simplified example, consider an open delta to open delta three phase transformer, where the 'open jaw' is between terminals A and C. Connect a resistor between terminals A and C. Clearly the full current flows in the AB and BC coils, both primary and secondary. However no current flows out of the B secondary terminal, and only minimal current flows into the B primary terminal.
In any case, I think a discussion about the functionality of the Leyton transformer connection should really be in its own thread, and not cluttering jake.hagm's first thread
-Jon
-Jon