Depending on the amplitude of the overcurrent, if it lasted several minutes, the bypass overcurrent protection should have tripped, not the UPS shut off..
ron said:Depending on the amplitude of the overcurrent, if it lasted several minutes, the bypass overcurrent protection should have tripped, not the UPS shut off..
I agree 100%, many UPS issues are caused by the poor battery maintenance. Even with good maintenance, the typical VLRA Batteries used in many UPS are prone to unpredictable failures. They are supposed to be inspected quarterly and have an annual PM per IEEE standards. With a single module/single battery system UPS, it is even more important.cschmid said:I think the problem you describing could be associated with battery maintenace..If the batteries are only lets say 50%..if the load is exceeded the machine will shut down..just because the machine says they are good does not mean they are at 100%..I am just throwing that out for an idea..
SmithBuilt said:My guys were doing some work at one of my customers. They have a Liebert UPS feeding their data center. It registered an over voltage and went on bypass (utility feeding the data center). They argue that we caused the shut down by shorting something out. My guys say they did nothing to cause the problem. They were not working on any circuits fed by the UPS nor anything live.
The customer rushed to the UPS and tried to get it back online. While they were doing this the UPS disconnected the power to the data center. They argue that they did not cause the shutdown. It cost them a lot of money and many unhappy customers.
My first question is what would cause an over voltage? Could a large load that is shut off cause it? A short? There was also talk of a couple of brownouts the same day.
Second, is it possible that the customer did make a mistake and shut off the power to the data center or the UPS malfunction? I'm researching the Liebert site now.
dbuckley said:Having the UPS room aircon fail is a good way of determining how hot static switches don't like to get. First the inverters stop, and the UPS goes into static bypass. All good so far. Then the static switch reaches its maximum allowable temperature, and thats when the data centre becomes eerily quiet...
dave__asdf said:also, do you know how much load was on the phase during normal operation before it tripped and what the rating of it is? i would guess that a 20a breaker supplied the motor or piece of equipment that is being blamed for the outage, but generally 20a of added load is not enough to put the liebert up to 150% (it is rated for 10 minutes @150%)
dave__asdf said:was it an input or output over voltage? or current?
the best thing to tell the customer is buy a new mitsubishi ups.