Is there any chart or calculation that i can use/follow to find out how much lighting per sqft is needed for certain places?? Thanks for the help.
You mean for load calcs?brother said:Is there any chart or calculation that i can use/follow to find out how much lighting per sqft is needed for certain places?? Thanks for the help.
Table 220.12 General Lighting Loads by Occupancy
Unit Load
Type of Occupancy Volt-Amperes per Square Meter Volt-Amperes per Square Foot
Armories and auditoriums 11 1
Banks 39b 3?b
Barber shops and beauty parlors 33 3
Churches 11 1
Clubs 22 2
Court rooms 22 2
Dwelling unitsa 33 3
Garages — commercial (storage) 6 ?
Hospitals 22 2
Hotels and motels, including apartment houses without provision for cooking by tenantsa 22 2
Industrial commercial (loft) buildings 22 2
Lodge rooms 17 1?
Office buildings 39b 3?b
Restaurants 22 2
Schools 33 3
Stores 33 3
Warehouses (storage) 3 ?
In any of the preceding occupancies except one-family dwellings and individual dwelling units of two-family and multifamily dwellings:
Assembly halls and auditoriums 11 1
Halls, corridors, closets, stairways 6 ?
Storage spaces 3 ?
aSee 220.14(J).
bSee 220.14(K).
M. D. said:here is another one,... I take it you meant you wanted recomendation for lighting
http://www.guth.com/products/pdf/t13-t19.pdf
Ahhh, it's a design thing.:wink: Sorry for the long and wrong post. The fact that your thread is in NEC threw me.brother said:yes i meant recommendation for the lighting.
chris kennedy said:Ahhh, it's a design thing.:wink: Sorry for the long and wrong post. The fact that your thread is in NEC threw me.
Not a problem. But take a close look. The 'lighting forum' is really the 'lightning forum'.:smile:brother said:sorry about that. shouldve been in the 'lighting forum'
chris kennedy said:Not a problem. But take a close look. The 'lighting forum' is really the 'lightning forum'.:smile:
Are you sure? Can I call channel 7 and tell them I have been struck by lightning dozens of times and have lived to tell about it?480sparky said:It is lightning, Chris.
It just strikes 120 times a second....![]()
M. D. said:here is another one,... I take it you meant you wanted recomendation for lighting
http://www.guth.com/products/pdf/t13-t19.pdf