What would be the potential hazard?
Faulty ungrounded switch leaving potential at the cover plate screws.
I've seen it more than once.
What would be the potential hazard?
coulter said:480 -
I thought about that - even as far as an intrinsicly safe control. I don't know how low you have to go to be safe when ones hands are soaking wet. Skin resistance gets pretty low when you are wet.
stick -
I was thinking if one wished to have the contol in the tub/shower area or for the area with the local amendment.
carl
Filthy Phil said:I was told by an inspector that if the switch was within reach of the shower the circuit had to be GFCI protected. This was aPITA because the panel didn't have room for a full sized GFCI breaker.
Filthy Phil said:I was told by an inspector that if the switch was within reach of the shower the circuit had to be GFCI protected. This was aPITA because the panel didn't have room for a full sized GFCI breaker.
JohnConnolly said:Faulty ungrounded switch leaving potential at the cover plate screws.
celtic said:Couldn't the same be said for any component?
480sparky said:Not if the strap is plastic.
480sparky said:Not if the strap is plastic.
Oklahoma City Amendments to 2002 NEC 210.70 (A) is hereby amended by adding the following sentence to the first paragraph, and adding a new exception:
The wall switch required for the lighting outlet in bathrooms shall be installed at least 5 feet (1.52m) measured horizontally, from a tub or shower.
Exception: The branch circuit supplying the bathroom lighting shall have ground-fault circuit-interrupter protection for personnel.
Is that hi-hat trim listed for wet location? If so what brand?480sparky said:Ya mean like this?
![]()
chris kennedy said:Is that hi-hat trim listed for wet location? If so what brand?
Looks like a damp location to me.chris kennedy said:Is that hi-hat trim listed for wet location? If so what brand?
chris kennedy said:Is that hi-hat trim listed for wet location? If so what brand?
celtic said:Couldn't the same be said for any component?
ItsHot said:Who Let The Engineer In Here?