They are just examples... and I'd say the intent is to just give typical scenarios. There's nothing in Code that says you can't have continuous lighting in residential or noncontinuous lighting in commercial/industrial. If you're doing the load calc', call 'em like you see 'em.
And you don't have to be an NFPA member to submit a proposal. Public Input is exactly that. But if you use the internet method, you must establish a user account on the NFPA website.
Thanks, that?s helpful info Smart$. Barring any suggestions from forum members, here?s what I?m considering as a proposal:
In Annex D, examples D1 through D3 treat General Lighting as continuous in a commercial occupancy and noncontinuous in residential occupancies. There is an implication that general lighting load may be energized for more than 3 hours in a store, but not in dwellings.
For proper and uniform component sizing, the examples in Annex D are widely referenced by electricians, by AHJ?s who enforce their own interpretations, by governmental testing agencies (i.e., states) who determine which electricians are competent to perform such calculations, by insurers who award or deny claims based on the NEC, and even by courts who rely on expert witnesses to determine whether a fire-damaged property had satisfied the minimum legal requirements as required by an adopted NEC.
In regards to the continuous nature of general lighting loads in commercial and residential occupancies, it would benefit the entire industry for NFPA to clarify their intent, either in these Annex D Examples, or perhaps in Article 220 (for example a footnote to Table 220.12).
Can anyone point out any flaws for me before I submit to NFPA?