A five story office has a footprint of 200 x 150.
Each floor will have 117 receptacle outlets.
What is the VA Load for the service of the building.
The Answer provided on the Test answers is 806,250 VA... I keep getting different at 525,000 VA for the Lighting.
Then for the receptacle load I get 66,000 VA.
Lighting Calculation
200 X 150 =30000 SQ. FT. x 5 Floors=150,000 SQ. Ft. Total x 3.5 from Table 220.12 For the Lighting Load. I got 525,0000 VA
Receptacle Calculation
Then Per 220.14K I tried 180VA X 117 Outlets x 5 Floors worth =105,300 Then The larger being 150,000 X 1 VA.Per Sq. FT. =150,000VA.
Now I derate The receptacle VA 150,000-10000=140000 X.40= 56,000Va
Now I add 525,000 VA From Lighting Load to 66,000 VA For the Receptacle Load. I get 591,000 VA Not 806,250 VA.
I really need to find what I'm doing Wrong...
Please any help is appreciated!
Each floor will have 117 receptacle outlets.
What is the VA Load for the service of the building.
The Answer provided on the Test answers is 806,250 VA... I keep getting different at 525,000 VA for the Lighting.
Then for the receptacle load I get 66,000 VA.
Lighting Calculation
200 X 150 =30000 SQ. FT. x 5 Floors=150,000 SQ. Ft. Total x 3.5 from Table 220.12 For the Lighting Load. I got 525,0000 VA
Receptacle Calculation
Then Per 220.14K I tried 180VA X 117 Outlets x 5 Floors worth =105,300 Then The larger being 150,000 X 1 VA.Per Sq. FT. =150,000VA.
Now I derate The receptacle VA 150,000-10000=140000 X.40= 56,000Va
Now I add 525,000 VA From Lighting Load to 66,000 VA For the Receptacle Load. I get 591,000 VA Not 806,250 VA.
I really need to find what I'm doing Wrong...
Please any help is appreciated!